Hi Allan,

On a previous thread, it seems that Surrette batteries like a fast charge periodically. At one time (as I recall) is was recommended to give them a C/5 once a week, but the company said that was not necessary. I don't know of C/13 to C/18 charges would be enough. Can your customer run the generator for a quick charge after cycling them down?

Drake

At 08:29 AM 8/2/2008, you wrote:
Did this customer check the voltage of the individual batteries/cells? Maybe there is a weak cell developing. Sometimes EQing can take a long time. I do not "buy" that batteries need to be cycled to stay healthy.

Todd

jay peltz wrote:

Hi Robert,

When you mention cycling batteries, are you saying that batteries in a offgrid system that are being cycled 15-25% a day should be cycled even deeper than that?

Thanks,

jay peltz power
On Aug 1, 2008, at 8:36 PM, robert ellison wrote:

A couple things that I haver noticed in the past, sometimes batteries like to be cycled, shut off the controllers and run them down, then charge them up fully and then give them an eq charge till it comes up the peak voltage and hold it there as it (sometimes) slowly rises. Any of these thoughts are superseded by Jamie if he has any thoughts. Also, if you have not given them an eq in a while it might take longer than the available solar time has to get them to the top and hold them there..
Have the controllers settings changed?

Bob
On Fri, Aug 1, 2008 at 10:18 PM, Allan Sindelar <[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>> wrote:

    Wrenches,
    In late 2003 we installed a 24V set of Rolls-Surrette 4-KS-21PS
    6V 1104 A/hr batteries in the off-grid system of a long-time
    client. The client's system had a democracy array of around 800
    watts of tracked PV. In early 2005 we added 1,280 watts of
    additional PV, and the client hasn't run the generator since; the
    system rarely drops below 80% and fills to 100% most days in
    sunny New Mexico. Batteries are located in a basement, so
    temperatures stay relatively constant, although it will vary
    slightly seasonally. MX60 controller is temperature compensated,
    with 29.6 VDC bulk and 31.4 VDC EQ set points.

    The problem is that the client reports being unable to achieve
    previous EQ voltages, and this inability appears to be a new
    development. The system is otherwise performing well. As the
    client is sharp and pays close attention to the system's
    operation, I'm not ready to blame user ignorance (with one
    possible exception; read on). This may be an issue of seasonally
    warm temperatures, but I'm not sure this would explain the full
    0.4 VDC reduction in voltage. I told him that I would post his
    problem to this list, and also request advice from Surrette Battery.

    Here is the client's description of the symptoms:
    I'm concerned that I am unable to equalize batteries at this
    time.  Up
    until June of this year the Tri-Metric readings during equalizing
    indicated
    holding voltage at 31.1, with maximum amps gain of around 52.
    Three weeks
    ago, when set on equalize, the maximum voltage reading was 30.7,
    with
    maximum amps of 46; this was reached around noon, and by around
    1:30 pm
    voltage/amps began its typical afternoon drop-off.  I attempted
    equalizing
    on two other occasions since then--the last time this past
    Saturday, with
clear skies up until mid-afternoon--but having the same results. So, the
    question is: are my batteries beginning their decline? We've had
    this set
    for 4 1/2 years, so it would seem a bit too early for this, given
    that these
    batteries are expected to last 7-10 years.

_______________________________________________
List sponsored by Home Power magazine

[email protected]

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
303-328-5533

_______________________________________________
List sponsored by Home Power magazine

[email protected]

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to