I presume there is a temp sensor on the CC and inverter.
And if the battery temps are higher then the voltage termination
would be lower which could explain it.
Or, I have seen them get off calibration which would cause a
difference in charge set points.
jay
peltz power
On Aug 2, 2008, at 10:29 AM, Drake Chamberlin wrote:
Hi Allan,
On a previous thread, it seems that Surrette batteries like a fast
charge periodically. At one time (as I recall) is was recommended
to give them a C/5 once a week, but the company said that was not
necessary. I don't know of C/13 to C/18 charges would be enough.
Can your customer run the generator for a quick charge after
cycling them down?
Drake
At 08:29 AM 8/2/2008, you wrote:
Did this customer check the voltage of the individual batteries/
cells? Maybe there is a weak cell developing. Sometimes EQing can
take a long time. I do not "buy" that batteries need to be cycled
to stay healthy.
Todd
jay peltz wrote: