I find the Outback FNDC has the ability to track the state of charge using net 
energy into the battery and net energy out.  Therefore one can use the SOC 
directly to start generator and charge batteries and not relay on battery 
voltage.  I have not used the Apollo for this purpose but believe it has the 
same capability.   

AS you know it is difficult to determine the state of charge either way.  If 
you charge to fast the charge efficiency is lowered, if you are drawing energy 
the battery voltage is lowered.  To find state of charge using the battery 
voltaqe requires you to know the resting voltage, a two to 8 hr wait after 
battery usage.  

What I try to do is to have the customer do due diligence, to take care of the 
batteries, but it rarely works.

Darryl


--- On Thu, 8/28/08, William Miller <[EMAIL PROTECTED]> wrote:

> From: William Miller <[EMAIL PROTECTED]>
> Subject: Re: [RE-wrenches] battery reference gen start module
> To: "RE-wrenches" <[email protected]>
> Date: Thursday, August 28, 2008, 4:07 PM
> Tump:
> 
> We use the XW inverter charger to battery level start
> generators.
> 
> William
> 
> 
> At 12:54 PM 8/28/2008, you wrote:
> >What are folks using to start generators using voltage
> parameters?