This is not a good combination of equipment choices. If you want a
safe and reliable installation it is good practice to use equipment
as it is intended to be used. You should not back feed an Xantrex XW
through the output side. The easiest way to go is use a Sunny Island
with the batteries in the garage instead of the XW. However if you
already have the XW in place then I would suggest using the Apollo
T80HV charge control as suggested by Daryl . It has a max of 200 VOC
at 80 amps . Why make it more complicated than it needs to be ?
Jon
Jon Haeme Innovations
Kempton, IL
NABCEP certified PV installer #102503-19
On Jan 18, 2009, at 11:31 PM, Jeff Yago wrote:
I know this subject has come up before, but there have been several
different suggested ways to handle the problem and I was hoping for
easiest. We install lots of both on grid and off grid systems.
However, we have a client that will require a ground mounted array
much futher away from the inverter and batteries in the garage than
we normally would want to do since the voltage drop for this long
distance would be excessive at low voltage even with large cables.
We have decided to locate a weather-proof sunnyboy grid-tie
inverter at the array, and supply 120/240 volts to the critical
loads sub-panel which is supplied by a Xanrex XW inverter and
battery bank in the garage. I realize there are several design
issues here when the grid is down, since we want the grid-tie
inverter to remain on but be blocked from the grid by the Xantrex
inverter.
The question is, what is the best way to keep a load on the
sunnyboy since it will not be grid connected during an outage.
Also, is there a best way to feed the output from the Sunnyboy to
the Xantrex that does not just power the sub-panel loads during an
outage, but also will re-charge the battery bank through the Xanrex?
If you back-feed the Xanrex from the sub-panel it is normally
supplying with output from the Sunnyboy, will the Xanrex see this
input and think the grid is up and be able to re-charge the battery
bank?
Will we need any separate transfer switches or power relays?
Thanks,
Jeff Yago
_____________________________________________________________
Netscape. Just the Net You Need.
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org