The best way is to use a SunnyIsland. It's all automatic - no need for
dummy loads.
Matt T
Jeff Yago wrote:
I know this subject has come up before, but there have been several different suggested ways to handle the problem and I was hoping for easiest. We install lots of both on grid and off grid systems. However, we have a client that will require a ground mounted array much futher away from the inverter and batteries in the garage than we normally would want to do since the voltage drop for this long distance would be excessive at low voltage even with large cables. We have decided to locate a weather-proof sunnyboy grid-tie inverter at the array, and supply 120/240 volts to the critical loads sub-panel which is supplied by a Xanrex XW inverter and battery bank in the garage. I realize there are several design issues here when the grid is down, since we want the grid-tie inverter to remain on but be blocked from the grid by the Xantrex inverter.
The question is, what is the best way to keep a load on the sunnyboy since it
will not be grid connected during an outage. Also, is there a best way to feed
the output from the Sunnyboy to the Xantrex that does not just power the
sub-panel loads during an outage, but also will re-charge the battery bank
through the Xanrex?
If you back-feed the Xanrex from the sub-panel it is normally supplying with
output from the Sunnyboy, will the Xanrex see this input and think the grid is
up and be able to re-charge the battery bank?
Will we need any separate transfer switches or power relays?
Thanks,
Jeff Yago
_____________________________________________________________
Netscape. Just the Net You Need.
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.176 / Virus Database: 270.10.9/1900 - Release Date: 1/18/2009 12:11 PM
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org