Hi Jeff,
1. if the distances are really far why not run the DC from the panels
to the inverter, higher voltage, smaller wire.
2. if you use the XW then yes you will be running the AC from the SB
to the sub panel, this will feed the inverter and cause it to charge,
which you will need to put a relay disconnect on. Use a SS relay on
the AC side from the SB connected to one of the XW aux relays. So you
are not really installing a load but a high battery/SB relay.
3. The XW will not see this as AC in. If you hook it up that way to
AC in it won't work except if the grid is on. No grid no SB. But
then also no battery charging.
Hope this helps,
jay
peltz power
On Jan 18, 2009, at 9:31 PM, Jeff Yago wrote:
I know this subject has come up before, but there have been several
different suggested ways to handle the problem and I was hoping for
easiest. We install lots of both on grid and off grid systems.
However, we have a client that will require a ground mounted array
much futher away from the inverter and batteries in the garage than
we normally would want to do since the voltage drop for this long
distance would be excessive at low voltage even with large cables.
We have decided to locate a weather-proof sunnyboy grid-tie inverter
at the array, and supply 120/240 volts to the critical loads sub-
panel which is supplied by a Xanrex XW inverter and battery bank in
the garage. I realize there are several design issues here when the
grid is down, since we want the grid-tie inverter to remain on but
be blocked from the grid by the Xantrex inverter.
The question is, what is the best way to keep a load on the sunnyboy
since it will not be grid connected during an outage. Also, is
there a best way to feed the output from the Sunnyboy to the Xantrex
that does not just power the sub-panel loads during an outage, but
also will re-charge the battery bank through the Xanrex?
If you back-feed the Xanrex from the sub-panel it is normally
supplying with output from the Sunnyboy, will the Xanrex see this
input and think the grid is up and be able to re-charge the battery
bank?
Will we need any separate transfer switches or power relays?
Thanks,
Jeff Yago
_____________________________________________________________
Netscape. Just the Net You Need.
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org