Kent:
Interesting...
What if the array is ground mount? I prefer not to have metallic conduit
underground. Fortunately, for off-grid we often have a combiner on the
rack that qualifies for a disconnecting means.
Also, off-grid Voc is on the order of 100 volts, as opposed to 400 to 600.
William
At 04:01 PM 6/7/2009, you wrote:
William,
It is interesting that the 2008 code also has the "utility-interactive"
typo. None the less, it is appropriate to put photovoltaic circuits in
metal conduit for off grid systems. The risk to fire fighters is nearly
the same in both cases.
Kent Osterberg
Blue Mountain Solar