William,

Metal is only required from the point that the PV circuit enters the building to the first accessible disconnect, outside the building plastic is okay.  For underground plastic is definitely best.  Here the inspectors have been happy with plastic being used inside the building for 3 or 4 feet from the floor up to the disconnect.  The rational is that a fire fighter us not likely to cut through it.

Yes, 100 volts isn't as much of a hazard as 400 to 600 volts.  But it is still a hazardous voltage and it makes nice arcs too.

I believe most combiner boxes don't qualify as a disconnect device because it takes a screw driver to open them before you can turn anything off.

Kent Osterberg
Blue Mountain Solar


William Miller wrote:
Kent:

Interesting...

What if the array is ground mount?  I prefer not to have metallic conduit underground.  Fortunately, for off-grid we often have a combiner on the rack that qualifies for a disconnecting means.

Also, off-grid Voc is on the order of 100 volts, as opposed to 400 to 600.

William



At 04:01 PM 6/7/2009, you wrote:
William,

It is interesting that the 2008 code also has the "utility-interactive" typo.  None the less, it is appropriate to put photovoltaic circuits in metal conduit for off grid systems.  The risk to fire fighters is nearly the same in both cases.

Kent Osterberg
Blue Mountain Solar
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org