Peter-

Appendix J of "PV and the NEC" covers this, too; as Kirpal said, you'll need to know the series fuse rating for the module first, though.
http://www.nmsu.edu/~tdi/pdf-resources/pdf%20version%20divided%20PV:NEC/APPENDIX%20J.pdf


-------- Original Message --------
Subject: Re: [RE-wrenches] String Combiners for a-Si modules
From: Peter Parrish <[email protected]>
To: 'RE-wrenches' <[email protected]>
Date: 2009/7/21 20:51

EPV Solar EVP-54

The Isc is 1.49 A

The cut sheet does not list a series fuse rating for the module.

But it does say something about being able to use up to 8 in parallel without external protection.

I am in the hunt for installation instructions.

- Peter


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
[email protected] <mailto:[email protected]> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
------------------------------------------------------------------------

*From:* [email protected] [mailto:[email protected]] *On Behalf Of *Kirpal Khalsa
*Sent:* Tuesday, July 21, 2009 3:11 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] String Combiners for a-Si modules

Peter...depending on the series fuse rating you might be able to get away with more strings in parallel before series fusing is required........what panels are they and what is the series fuse rating of the modules? Fronius has a white paper explaining when series fusing is required and when you can get by without.......it all relates to series fuse rating and Isc......the higher the series fuse rating and the lower the Isc the more strings you can parallel with out adding series fusing........
--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com <http://www.oregonsolarworks.com>
541-218-0201 m
541-592-3958 o

On Tue, Jul 21, 2009 at 2:44 PM, Peter Parrish <[email protected] <mailto:[email protected]>> wrote:

We are doing an engineering design for a large scale PV ground mount system
based on a-Si modules. Since the Isc of the modules is 1.5 A, instead of 7-8
A of typical c-Si modules, are there special low-current combiners out
there? Does each string need an overcurrent protection device? Any help with
a-Si based system design would be greatly appreciated.


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
[email protected] <mailto:[email protected]>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected] <mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>




------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to