Max,

 

I’m not sure I understand your scenario completely. The WEEB-Lug, superior to 
the ILSCO product, is intended for grounding the rack to the equipment 
grounding conductor. Each rail gets a WEEB-Lug and an EGC ties all those rails 
together and takes the ground to the j-box to enter the conduit system (don’t 
like combiner boxes on residential rooftops). The key is how to effectively 
bond metal conduit. Bonding bushings or box fittings are the only means I know 
of to do this. As others have pointed out, the bushings currently on the market 
are often not designed for outdoor use. This is particularly of concern in high 
corrosion areas (where EMT is not recommended). 

 

My experience is that it is better to bond with indoor lugs than not to bond at 
all. When I check old lugs in the field with cad-plated set screws, they often 
still have a good bond even though the screw is fully rusted. The key is the 
bond between the conductor and the lug, and the between the lug and the metal 
it is attached to. If both surfaces are tight and no oxygen is getting to the 
interfaces, the bond will stay for a very long time—possibly the life of the 
system in a lower corrosion environment. The set screw is mechanical pressure, 
not the bonding point—rust  locks it..  It is best to use outdoor-rated 
equipment, but in some cases, it may be impossible because the equipment may 
not be manufactured, since the market is too small. Oh the joys of exterior 
wiring.

 

Bill.

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Max Balchowsky
Sent: Monday, October 12, 2009 6:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

 

Bill, what about using the weeb bonding method for the panels, conduit between 
sub arrays with mineralac clamps and then the weeb grounding lug for 
the ground wire to the combiner box and then home to the panel. The only time 
this has been an issue is where the jurisdiction doesn't accept the Wiley 
product.....
(I never liked what the sun does to PVC conduit)



Max Balchowsky
SEE Systems
760-403-6810 

  

  _____  

From: Bill Brooks <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Friday, October 9, 2009 10:20:19 AM
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays




August and Max,

 

If all you are doing in supporting the conductors, PVC conduit is sufficient 
with protective bushings on each end. Once you go to EMT, then grounding 
bushings must be installed at both ends and the EGC needs to pick up those 
bushings. More expensive and time consuming, but it looks better and you can 
span a greater distance. 

 

Bill.

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Max Balchowsky
Sent: Thursday, October 08, 2009 8:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

 

August - we've been using 1/2" emt between arrays with plastic bushings to 
protect wires and a dual "minerallac" clamps ( 
http://minerallac.thomasnet.com/viewitems/pipe-fasteners/ll-categories-cully-pipe-fasteners-conduit-hangers?
 
<http://minerallac.thomasnet.com/viewitems/pipe-fasteners/ll-categories-cully-pipe-fasteners-conduit-hangers?&bc=100%7C1006%7C1281&forward=1>
 &bc=100%7C1006%7C1281&forward=1) to tie the conduits to the riser on the array 
support. Has worked well over the years and the inspectors like the "bond" 
between the arrays.....

  _____  

From: August Goers <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Thursday, October 8, 2009 11:07:08 AM
Subject: [RE-wrenches] Rooftop wiring methods between multiple subarrays



Hi Wrenches,

 

I’m looking for fresh ideas on how to run USE-2 wires between subarrays on 
rooftops. Let’s say we have a flat roof commercial system with dozens of 
separate rows of modules. How would you folks run the USE-2 wiring between 
these arrays? We’ve been using J-boxes and EMT which is robust but time 
consuming. I’ve also used strut with a cap strip on the top which effectively 
makes a wire raceway but it is difficult to properly ground both ends of the 
raceway and is also time consuming. 

 

Looking forward to hearing your ideas. Best, August 

 

August Goers

 

Luminalt Energy Corporation

O: 415.564.7652

M: 415.559.1525

F: 650.244.9167

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to