Max,

 

Is the Minerallac clamp really rated as a bonding device? I don’t think so. It 
may make an electrical connection, but I don’t think it is nearly as good as a 
ground bushing. It is also made of cad-plated steel and I don’t think it is as 
durable as EMT or a ground bushing with a cad plated fastener. It probably 
doesn’t matter too much if it is just protecting conductors and a bonding 
conductor between two rails, but I would not want to rely on this for any 
circuits containing the final equipment grounding conductor or main circuit 
conductors. Not something I would lose a whole lot of sleep over—there are far 
bigger issues to solve. Of far more significance is the overall wire management 
of USE-2 conductors in the array. Structure suppliers still do a terrible job 
of providing an effective means of controlling and protecting conductors—this 
is nearly a decade after the first commercially available system was developed. 
Is anyone else ticked off about this???

 

Bill.

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Max Balchowsky
Sent: Wednesday, October 14, 2009 2:59 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

 

Bill, as you know, if the array is on a tilted roof (tile track bkts or fast 
jacks) and the array is monolithic, all the wires go directly from under the 
panels to the junction box ( I mis-spoke when I said Combiner box, I too don't 
see the need for combiner boxes on residential systems ).We go directly from 
the weeb ground lug into the junction box then down. The panels are bonded to 
the rails with the  Weeb Bonding Clips.  If the array consists of tilted rows, 
we've used either a bare copper wire tie wrapped to the EMT between rows or run 
in the EMT (most rows are 18-24" apart depending on angle). What I've done on 
the last couple of tilted row residential jobs is used the mineralac clamps and 
EMT between rows (inspector has bought it as a "bond" between rows then used 
the ground lug on the last row to take the ground into the junction box and 
down..........

Max

 

  _____  

From: Bill Brooks <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Tuesday, October 13, 2009 7:59:13 AM
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays




Max,

 

I’m not sure I understand your scenario completely. The WEEB-Lug, superior to 
the ILSCO product, is intended for grounding the rack to the equipment 
grounding conductor. Each rail gets a WEEB-Lug and an EGC ties all those rails 
together and takes the ground to the j-box to enter the conduit system (don’t 
like combiner boxes on residential rooftops). The key is how to effectively 
bond metal conduit. Bonding bushings or box fittings are the only means I know 
of to do this. As others have pointed out, the bushings currently on the market 
are often not designed for outdoor use. This is particularly of concern in high 
corrosion areas (where EMT is not recommended). 

 

My experience is that it is better to bond with indoor lugs than not to bond at 
all. When I check old lugs in the field with cad-plated set screws, they often 
still have a good bond even though the screw is fully rusted. The key is the 
bond between the conductor and the lug, and the between the lug and the metal 
it is attached to. If both surfaces are tight and no oxygen is getting to the 
interfaces, the bond will stay for a very long time—possibly the life of the 
system in a lower corrosion environment. The set screw is mechanical pressure, 
not the bonding point—rust  locks it..  It is best to use outdoor-rated 
equipment, but in some cases, it may be impossible because the equipment may 
not be manufactured, since the market is too small. Oh the joys of exterior 
wiring.

 

Bill.

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]