This brings up another question for me: what really is the difference in the 
armor between AC and MC, and how come AC isn't being allowed, or is it allowed, 
but not specifically mentioned, being considered a metal (metallic?) enclosure?

R. Walters
[email protected]
Solar Engineer




On Dec 5, 2009, at 8:45 AM, Dave Click wrote:

> I believe that in a Code Corner back in the '05 era, John Wiles had said that 
> MC cable was OK to use, then in a later Code Corner he says that it isn't; I 
> thought it was because part of the reason for a metal raceway is physical 
> protection, and EMT/FMC would be sturdier than MC. But then I looked at the 
> 2011 Code, which (as it currently stands) will allow MC:
> 
> (E) Direct-Current Photovoltaic Source and Output Circuits Inside a Building. 
> Where dc photovoltaic source or output circuits from a building-integrated or 
> other photovoltaic system are run inside a building or structure, they shall 
> be contained in metal raceways, Type MC metal clad cable that complies with 
> 250.118(10), or metal enclosures, from the point of penetration of the 
> surface of the building or structure to the first readily accessible 
> disconnecting means. The disconnecting means shall comply with 690.14(A), 
> (B), and (D). [ROP 4-228]
> 
> The new 690.31(E) is about ten times longer than the '08 edition, now 
> requiring the conduit to be >10" below the surface of the roof (to avoid 
> firefighting equipment venting the roof) and labeling along that conduit too:
> http://www.solarabcs.com/index.php?option=com_docman&task=doc_download&gid=248&&Itemid=72
> 
> And to save you a lookup:
> 250.118 Types of Equipment Grounding Conductors.
> The equipment grounding conductor run with or enclosing the circuit 
> conductors shall be one or more or a combination of the following:
> ...
> (10)  Type MC cable where listed and identified for grounding in accordance 
> with the following:
> a.    The combined metallic sheath and grounding conductor of interlocked 
> metal tape–type MC cable
> b.    The metallic sheath or the combined metallic sheath and grounding 
> conductors of the smooth or corrugated tube-type MC cable
> 
> -------- Original Message --------
> Subject: Re: [RE-wrenches] 690.32(E) + MC?
> From: R Ray Walters <[email protected]>
> To: RE-wrenches <[email protected]>
> Date: 2009/12/5 03:28
> 
>> I think the issue here is 690.32 deals just with 'fittings and
>> connectors', not the actual wire or cable. I believe you meant to
>> reference 690.31 which says 'all raceway and cable wiring methods
>> included in this code....shall be permitted'. But you still have to
>> comply with 690.31E which says it needs to be in 'metal raceways or
>> metal enclosures' once it enters the building up to the first readily
>> accessible disconnect. Looking at article 100, the definition of
>> raceway does include flexible metal conduit, so it seems you could
>> use metal flex conduit and pull wire, but I know many inspectors
>> still won't allow it. Reading up in articles 320 and 330 for AC and
>> MC cables, MC doesn't say it's conduit, so it would be out, but AC
>> says its enclosed in a 'flexible metallic enclosure'. So now the
>> question is: Is metallic the same as metal? (Oh Boy are we splitting
>> semantic hairs now.......). Bill or William are the ones to clarify
>> better than I on all of this, though. They've been involved in the
>> actual writing of the code. IMHO, it seems yet another point to be
>> clarified in future additions of the code. Meanwhile to be safe, most
>> of us are just running EMT once we penetrate the building. (which
>> opens yet another question: when have you penetrated the building?
>> above or below the roof flashing?)
>> I think I've caused enough trouble for now,
>> R. Walters [email protected] Solar Engineer
>> On Dec 4, 2009, at 7:47 PM, Darryl Thayer wrote:
>>> I have always read metal conduit, The reason being the solar is
>>> unfused source circuits, and there is no way for overcurrent
>>> protective devices to open.  Therefore, the conductors must be
>>> protected from starting a fire under conditions of continuous
>>> overcurrent. darryl
>>> --- On Fri, 12/4/09, [email protected]
>>> <[email protected]> wrote:
>>>> From: [email protected] <[email protected]> Subject:
>>>> [RE-wrenches] 690.32(E) + MC? To: "RE-wrenches"
>>>> <[email protected]> Date: Friday, December 4,
>>>> 2009, 5:18 PM I did a project a while ago for a supplier /
>>>> Installing out fit (who has their in house engineering types),
>>>> who told me that either MC or maybe AC cable did comply with
>>>> 690.32E. today I'm being told that's not the case, and I can't
>>>> seem to put my finger on it ... any pointers? thanks db
>>>> Dan Brown President Foxfire Energy Corp. Renewable Energy Systems
>>>> (802)-483-2564 www.Foxfire-Energy.com NABCEP #092907-44
>>>> -----Inline Attachment Follows-----
>>>> _______________________________________________ List sponsored by
>>>> Home Power magazine
>>>> List Address: [email protected]
>>>> Options & settings: 
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> List rules & etiquette: www.re-wrenches.org/etiquette.htm
>>>> Check out participant bios: www.members.re-wrenches.org
>>> _______________________________________________ List sponsored by
>>> Home Power magazine
>>> List Address: [email protected]
>>> Options & settings: 
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> List rules & etiquette: www.re-wrenches.org/etiquette.htm
>>> Check out participant bios: www.members.re-wrenches.org
>> _______________________________________________ List sponsored by
>> Home Power magazine
>> List Address: [email protected]
>> Options & settings: 
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> List rules & etiquette: www.re-wrenches.org/etiquette.htm
>> Check out participant bios: www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to