To stir the pot a little further.. as Ray mentioned.. article 320.2 defines an armored cable as being "in a flexible metallic enclosure", which currently satisfies 2008 690.31(E) requirements. (as interpreted by some). where as 2008 330.2 defines MC as being "enclosed in an armor of interlocking metal tape, or a smooth or corrugated metallic sheath". I'm also told some AC cable is aluminum jacketed with a grounding conductor woven into the jacket? and what about the thread of the possibility of grounded metal being a source of ignition -- pyrophoric carbonization? Would this suggest DC ark fault devices at each source? Does anyone even make such a critter? OK -- how about a color code for Solar Source circuits? I nominate orange? -- that's the color code they use in Hybrid cars. so, firefighters are trained not to cut thru anything orange. Just stirring away. db
Dan Brown
President
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44
-------- Original Message --------
Subject: Re: [RE-wrenches] 690.32(E) + MC?
From: R Ray Walters <[email protected]>
Date: Sun, December 06, 2009 6:50 pm
To: RE-wrenches <[email protected]>
This brings up another question for me: what really is the difference in the armor between AC and MC, and how come AC isn't being allowed, or is it allowed, but not specifically mentioned, being considered a metal (metallic?) enclosure?
R. Walters
[email protected]
Solar Engineer
On Dec 5, 2009, at 8:45 AM, Dave Click wrote:
> I believe that in a Code Corner back in the '05 era, John Wiles had said that MC cable was OK to use, then in a later Code Corner he says that it isn't; I thought it was because part of the reason for a metal raceway is physical protection, and EMT/FMC would be sturdier than MC. But then I looked at the 2011 Code, which (as it currently stands) will allow MC:
>
> (E) Direct-Current Photovoltaic Source and Output Circuits Inside a Building. Where dc photovoltaic source or output circuits from a building-integrated or other photovoltaic system are run inside a building or structure, they shall be contained in metal raceways, Type MC metal clad cable that complies with 250.118(10), or metal enclosures, from the point of penetration of the surface of the building or structure to the first readily accessible disconnecting means. The disconnecting means shall comply with 690.14(A), (B), and (D). [ROP 4-228]
>
> The new 690.31(E) is about ten times longer than the '08 edition, now requiring the conduit to be >10" below the surface of the roof (to avoid firefighting equipment venting the roof) and labeling along that conduit too:
> http://www.solarabcs.com/index.php?option=com_docman&task=doc_download&gid=248&&Itemid=72
>
> And to save you a lookup:
> 250.118 Types of Equipment Grounding Conductors.
> The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
> ...
> (10) Type MC cable where listed and identified for grounding in accordance with the following:
> a. The combined metallic sheath and grounding conductor of interlocked metal tape–type MC cable
> b. The metallic sheath or the combined metallic sheath and grounding conductors of the smooth or corrugated tube-type MC cable
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] 690.32(E) + MC?
> From: R Ray Walters <[email protected]>
> To: RE-wrenches <[email protected]>
> Date: 2009/12/5 03:28
>
>> I think the issue here is 690.32 deals just with 'fittings and
>> connectors', not the actual wire or cable. I believe you meant to
>> reference 690.31 which says 'all raceway and cable wiring methods
>> included in this code....shall be permitted'. But you still have to
>> comply with 690.31E which says it needs to be in 'metal raceways or
>> metal enclosures' once it enters the building up to the first readily
>> accessible disconnect. Looking at article 100, the definition of
>> raceway does include flexible metal conduit, so it seems you could
>> use metal flex conduit and pull wire, but I know many inspectors
>> still won't allow it. Reading up in articles 320 and 330 for AC and
>> MC cables, MC doesn't say it's conduit, so it would be out, but AC
>> says its enclosed in a 'flexible metallic enclosure'. So now the
>> question is: Is metallic the same as metal? (Oh Boy are we splitting
>> semantic hairs now.......). Bill or William are the ones to clarify
>> better than I on all of this, though. They've been involved in the
>> actual writing of the code. IMHO, it seems yet another point to be
>> clarified in future additions of the code. Meanwhile to be safe, most
>> of us are just running EMT once we penetrate the building. (which
>> opens yet another question: when have you penetrated the building?
>> above or below the roof flashing?)
>> I think I've caused enough trouble for now,
>> R. Walters [email protected] Solar Engineer
>> On Dec 4, 2009, at 7:47 PM, Darryl Thayer wrote:
>>> I have always read metal conduit, The reason being the solar is
>>> unfused source circuits, and there is no way for overcurrent
>>> protective devices to open. Therefore, the conductors must be
>>> protected from starting a fire under conditions of continuous
>>> overcurrent. darryl
>>> --- On Fri, 12/4/09, [email protected]
>>> <[email protected]> wrote:
>>>> From: [email protected] <[email protected]> Subject:
>>>> [RE-wrenches] 690.32(E) + MC? To: "RE-wrenches"
>>>> <[email protected]> Date: Friday, December 4,
>>>> 2009, 5:18 PM I did a project a while ago for a supplier /
>>>> Installing out fit (who has their in house engineering types),
>>>> who told me that either MC or maybe AC cable did comply with
>>>> 690.32E. today I'm being told that's not the case, and I can't
>>>> seem to put my finger on it ... any pointers? thanks db
>>>> Dan Brown President Foxfire Energy Corp. Renewable Energy Systems
>>>> (802)-483-2564 www.Foxfire-Energy.com NABCEP #092907-44
>>>> -----Inline Attachment Follows-----
>>>> _______________________________________________ List sponsored by
>>>> Home Power magazine
>>>> List Address: [email protected]
>>>> Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> List rules & etiquette: www.re-wrenches.org/etiquette.htm
>>>> Check out participant bios: www.members.re-wrenches.org
>>> _______________________________________________ List sponsored by
>>> Home Power magazine
>>> List Address: [email protected]
>>> Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> List rules & etiquette: www.re-wrenches.org/etiquette.htm
>>> Check out participant bios: www.members.re-wrenches.org
>> _______________________________________________ List sponsored by
>> Home Power magazine
>> List Address: [email protected]
>> Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> List rules & etiquette: www.re-wrenches.org/etiquette.htm
>> Check out participant bios: www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________ List sponsored by Home Power magazine
List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org