Ray,
Sorry, I'm not buying that argument over a 25+ year design lifespan. Also, -and 
perhaps something many folks don't consider- the NEC requires a MAX loss of ≤5% 
over the ENTIRE circuit. That means all the way to the mains panel. Best 
practices would require no more than 1.5% VD between the inverter and the mains 
so as to avoid any potential of overvoltage disconnection by the inverter. As 
it tries to push the current into the grid, it also pushes up the voltage on 
that line and on it's own sensors. Obviously, the larger the current flow and 
the higher the VD, the worse the situation could be. Bear in mind that the grid 
is not held to the same over and under voltage specifications as your inverter 
is. 3% + 1.5% is pushing it just a bit too close for comfort and I still think 
wasting watts in wire losses is bad design. We agree that orienting PVs to an 
azimuth other than 180° and a bit less than latitude elevation is less than 
ideal, but you "run what you brung" in terms of the orientation and roof pitch 
of a structure. Better to take a hit on production if we're talking about the 
backasswards method of incentivizing by the installed watt, than not installing 
PV at all. That said, we DO have control over wire sizing. IMO, throwing away 
watts forever just to cheapen it up a very little bit upfront is poor economy 
and as the price of gird supplied power increases over the years, the waste and 
lost revenue is even more acerbated.
Best, Bob-O

On Apr 6, 2010, at 6:04 PM, R Ray Walters wrote:

Just run the numbers sometime. Compare the cost difference of #6 vs. #4 wire 
say, and then look at how many more watts you're actually saving, then multiply 
that additional wattage by the installed cost per watt. 
Very simply, once you've satisfied code requirements, there is a point at which 
it is cheaper to add more panels than use bigger wire.
Also, that point is a moving target that fluctuates with PV and wire costs. 
I've found recently for our projects, that that point is falling at about 3% 
loss.
I also include a cost factor for oversizing the conduit, extra labor (bigger 
wire is harder to handle), and any connectors needed to land the larger wire.
I've got very well designed systems working for decades, using this method. 
This is how large commercial systems are designed as well. 
You can't simply pull 1%, and then call us bad designers because we actually do 
an economic analysis for each wire run.
It used to be unheard of to install PV facing anything but due south at 
latitude tilt, but now we know to add a few more modules. Same concept.

R. Walters
[email protected]
Solar Engineer




On Apr 6, 2010, at 1:37 PM, Bob-O Schultze wrote:

> Ray,
> A 2% wire loss is the generally accepted metric for battery based systems 
> with relatively low PV voltage input (<150Voc). It's just plain bad design to 
> accept more than a 1% VD on higher voltage systems. PVs ain't THAT cheap.
> Best, Bob-O
> 
> On Apr 6, 2010, at 11:44 AM, R Ray Walters wrote:
> 
> 
> Once I have fulfilled NEC min. requirements, I use a spreadsheet to analyze 
> the cost of larger wire vs. the cost of power lost. Going under 2% is usually 
> not worth it, if copper prices are high, and PV cost is low enough (current 
> market). Sizing for under 2% was good economics a few years back, when PV was 
> high, and copper was low, though.
> 
> For NEC 2011, I agree: while I readily welcome development of DC AFI, 
> implementing code before the technology is ready, is a bad idea. But that may 
> be the only way to get the technology in place.....
> 
> Ray
> 
> On Apr 6, 2010, at 11:15 AM, Kent Osterberg wrote:
> 
>> Ray,
>> 
>> Considering that we design PV wiring to be efficient with voltage (and 
>> power) loss typically less than 2%, the wire size is nearly irrelevant to 
>> arcing issues.   Essentially all the energy available from the PV array can 
>> be dissipated in the dc arc.   And since the current is limited by the 
>> nature of the IV curve, breakers alone usually won't clear the fault.  The 
>> best combiner breakers can do (if you have enough parallel circuits) is 
>> isolate the fault to one string in the PV array.  With one string being 1 or 
>> 2 kW in many systems there is still the potential for a lot of heat.
>> 
>> With the 2011 code just around the corner and no dc arc fault protection on 
>> the horizon, it looks like our industry is again going to have a code 
>> requirement that no one can fulfill.  
>> 
>> Kent Osterberg
>> Blue Mountain Solar, Inc.
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to