Chris,
I've seen a bladder tank modulate the "shut-down" process in a
up-the-hill gravity feed tank when using a (IMO) more reliable float valve
rather than a float switch. Watts model number 1250 is an example of a toilet
tank method of stopping/starting flow to a tank. With the bladder tank and a
standard issue Sq D. pressure switch (in the vicinity of the wellhead) it seems
to be a pretty bomb -proof set-up.
Bill Battagin
Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA 95983
530-284-7849/6544 fax
----- Original Message -----
From: Chris Worcester
To: [email protected] ; 'RE-wrenches'
Sent: Wednesday, June 16, 2010 1:34 PM
Subject: Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump
Great ideas on load management to save the DC/AC system sizing. I haven’t
spent time researching their need for this 3hp pump or age and all, but
definitely worth looking at that side. Since it does pump to the 3000g gravity
feed tank up the hill. What’s strange is there is still a bladder tank in the
garage, possibly decommissioned when they added the gravity system.
Sincerely,
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
[email protected]
"Proven Energy Solutions"
From: [email protected]
[mailto:[email protected]] On Behalf Of Allan Sindelar
Sent: Tuesday, June 15, 2010 8:48 PM
To: [email protected]; RE-wrenches
Subject: Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump
Chris,
We deal with deep wells routinely.
Recently we installed a GTWB system for a very enjoyable retired couple.
Their needs included the goat milker, sheep barn, two freezers and a fridge,
and irrigation well pump, with the system sized for continuous operation in the
event of a long-term (i.e. permanent) loss of the grid. This was on one acre in
the suburbs south of Albuquerque. We used an XW4548, as it was the only
battery-based, 120/240, single-inverter, grid-tie unit available currently.
As part of the normal load-reduction process, we determined that the 2hp
conventional well pump could be replaced with a 1hp soft-start SQ and have
adequate head and flow for their sprinklers. Changing out the pump way more
than paid for itself in the amount of inverter capacity we didn't need.
I would encourage you to look at both of these related issues carefully as
part of this situation: could a smaller pump meet the head and flow
requirements of this site, and is a soft-start pump available? Usually, if an
inverter or stack of them can't handle a big inductive load like a conventional
pump, it's because of the starting surge. I suspect a smaller soft-start pump
may be doable in your situation.
Allan
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
Hello offgrid Wrenches,
I just inherited an off grid system with one VFX3524 inverter running the
home loads, and a 17kW Guardian Generac they use for charging (through an X-240
back into the inverter) & to run their Franklin 3hp 240 VAC well pump, S. F.
max amp 17.0 ( rated on its controller)
This is a really convoluted system as they have another 120/240 VAC
Transformer to have the inverter talk to the 240 volt signal the gen set needs
to see. Yikes.
So I am proposing to add a second inverter if it can run the well pump and
eliminate the extra transformer. This will also reduce gen set run time in half
while battery charging, a big plus with the nice 24V Hawker battery bank, 1020
AH at the 6 hour rate.
There aren’t any other unusual large AC loads in the home, just the fridge,
washer, computer, and such. LPG for cooking, water heating, clothes dryer.
Thanks in advance for all ideas here!
Sincerely,
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
[email protected]
"Proven Energy Solutions"
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
------------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.437 / Virus Database: 271.1.1/2941 - Release Date: 06/16/10
06:35:00
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org