Hi Kurt,

A very good idea.

Do you know how much more efficient the 3 phase is vs the single?

Thanks,

jay

peltz power


On Jun 24, 2010, at 10:41 AM, Kurt Albershardt wrote:

> Once you determine the real pump requirements (as others have mentioned, this 
> is critical - IME particularly if the "well guy" sized and sold the pump) and 
> if a larger than SQflex pump is needed, I have had good luck using VFDs to 
> drive three-phase pumps with single phase power.  You can pay Franklin the 
> big $$ for their system, but a commodity VFD from someone like Automation 
> Direct will set you back about $100/HP and (up to 3 HP) will accept single 
> phase input power.  This gets you sophisticated motor protection, 
> programmable ramp soft starts, restart delays, and a plethora of input and 
> output terminals for shutdown switches, PID sensor inputs, etc. and will 
> allow you to create all manner of interesting system behavior.  Most also 
> include a (software programmable) runtime limitation or alarm which can 
> prevent  scenarios like Chris described below.  3-phase motors are more 
> efficient anyway so I seriously doubt we will sell a traditional single phase 
> pump or fan again.
> 
> 
> 
> 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to