Jason,

Now you are opening up a can of worms.

It's bad enough that 705.12(D) doesn't say anything about a panel that can't (or shouldn't, or won't) have anything connected but interactive inverters. But when that is the case, a bus rating of 100% of the source circuits should apply. For PV systems a 125% factor will already apply to each inverter circuit.

While it seems logical that the conductors are an extension of the bus bar and should be treated the same way, 705.12(D) isn't about the conductors - it's about the bus bars. The conductors are protected by the breakers -- 80-amp breakers and wire with 80-amp ampacity. 

Getting into the example further, I see flaws in it. If the inverters are 7500-watt 240-volt, the output current would be 7500/240 = 31.25 amps and 40-amp breakers would be adequate. Then there would have been no issues, even going directly into the main panel. If the inverters are 7500-watt 208-volt, the output current is 7500/208 = 36 amps and the 50-amp breakers make sense. That means the bus bars and feeder conductor have a continuous current of 72 amps.  That means neither the 80-amp breaker nor 80-amp wire is sufficient because 72 x 1.25 = 90 amps. Now the example doesn't resolve the limitation of backfeeding at the main. Opps!

Kent Osterberg
Blue Mountain Solar






Jason Szumlanski wrote:

Another key is to remember that this discussion also applies to the conductor between the main panel and subpanel. In a large PV system, this could result in a pretty large wire between the two panels, and a significant cost that is often overlooked. In some cases it makes sense to locate the subpanel close to the main panel and run multiple sets of smaller wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection connected to the inverters, adding a main breaker (theoretically 80A in this example) in the subpanel doesn’t change things. Even though this wire would be theoretically protected by an 80A breaker at each end, you can’t size the wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not that it makes much of a difference in this example, but it still must be considered)

 

At least that’s how I understand it…

 

Jason Szumlanski

Fafco Solar

 

 

From: [email protected] [mailto:[email protected]] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase system shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply per bar.

 

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

 

 


From: [email protected] [mailto:[email protected]] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 - 50A breakers.


Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

 

 


From: [email protected] [mailto:[email protected]] On Behalf Of Kent Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the premises. So the question becomes: is the sub-panel capable of supplying branch circuits or feeder loads? If yes, then the sum of the breakers (potentially) feeding the bus is 180 amps so a 150-amp rating is required and the inverters would have to feed the opposite end of the bus bars. If no, the code is not clear on the requirement, but obviously the 80-amp breaker in the main panel limits the maximum current flowing through the sub-panel.

Kent Osterberg
Blue Mountain Solar


_______________________________________________ List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to