By this argument, wouldn't it be necessary to check every conductor in the
backfeed path adding potential PV amps to their required ampacity including
the utility conductor from the transformer?
 
Kris

Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
[email protected]
www.legacysolar.com 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 1:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultiple
inverter outputs



Here is a 690.64(B)(2) opinion from Wiles that may help. 

http://www.fafcosolar.com/download/409/690%2064%28B%29%282%29TECH-1.pdf

 

It's still my contention that the conductors need to be sized for 150A in
this example, unless an exception is made by the AHJ. If David Brearley's
post about Wiles' clarification is accurate, them the 80A main breaker in
the subpanel can be used for calculations, but the conductor still needs to
be sized for 80A + 80A =160A / 1.2 = 133.3A.

 

Jason

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Kent
Osterberg
Sent: Wednesday, March 30, 2011 12:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

 

Al,

How about a 15-amp single-pole breaker for power line carrier communications
equipment to talk to the inverters?
Technically, I think either way they are loads and that changes everything.
But in my opinion they are minor and should be allowed without considering
the sum of all sources.

Kent Osterberg
Blue Mountain Solar


Al Frishman wrote: 

Is a monitoring system installed in the Load Center to measure the
cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that go around the
conductors and the Voltage ref is taken by attaching conductors to each
phase, the Neutral and the ground bar.    The digital Meter has a 3-pole 5A
breaker in it so the conductors in the load center can be connected to lugs
on the bus bar directly.

 

Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com <http://www.aeonsolar.com/> 

 

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system, this
could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense to
locate the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection connected to
the inverters, adding a main breaker (theoretically 80A in this example) in
the subpanel doesn't change things. Even though this wire would be
theoretically protected by an 80A breaker at each end, you can't size the
wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
that it makes much of a difference in this example, but it still must be
considered)

 

At least that's how I understand it.

 

Jason Szumlanski

Fafco Solar 

 

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase system
shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply per
bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is required
and the inverters would have to feed the opposite end of the bus bars. If
no, the code is not clear on the requirement, but obviously the 80-amp
breaker in the main panel limits the maximum current flowing through the
sub-panel. 

Kent Osterberg
Blue Mountain Solar

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to