If your Inspector dude specifically sited 690.4.(B), and you are talking about an AC inverter output circuit back to the main service panel, I'd say your Inspector is having a bad day (or you seriously p#ssed him off). Figure 690.1(A) clearly distinguishes between PV Source / Output circuits (DC) and Inverter Output circuits (AC). Sounds like you're dealing with the later. in which case 690.4(B) does not apply. should be the same as if you were running any two normal sub feeders (article 215, 300,110.. the usual suspects). 690.3 says 690 trumps. (that will really p#iss him off). but you do have all the 705 stuff mentioned in 690.3 to deal with (in addition to 705.60). is this in Vt?.. db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44
-------- Original Message --------
Subject: Re: [RE-wrenches] 690.4 (B) ???
From: "Kirk Herander, VSE" <[email protected]>
Date: Sat, April 09, 2011 9:29 pm
To: <[email protected]>, "'RE-wrenches'"
<[email protected]>
PS Does this merely mean that conductors from more than one source must be
bundled("connected") together, but are allowed in the same conduit?
Kirk Herander
Vermont Solar Engineering
802.863.1202
NABCEP(tm) Certified Solar Installer
NYSERDA-eligible Installer
VT Solar Incentive Program Partner
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Kirk
Herander, VSE
Sent: Saturday, April 09, 2011 9:10 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] 690.4 (B) ???
2008 NEC states that:
(B) Conductors of Different Systems. Photovoltaic
source circuits and photovoltaic output circuits shall not be
contained in the same raceway, cable tray, cable, outlet box,
junction box, or similar fitting as feeders or branch circuits
of other systems, unless the conductors of the different systems
are separated by a partition or are connected together.
Can anyone describe and give an example of what "connected together" means
to inverter PV circuits in the same conduit as a branch (load) circuit?
I have a single existing PVC conduit to a barn with an AC load subpanel. I
want to run the output conductors of an inverter combiner panel in the barn
through the same conduit to get to be main building. The fill / derating
calcs work to do this. The inspector says I have to run a new conduit for
the AC inverter combiner because the subpanel feeder and the combiner output
conductors are "not connected". But they are both connected to the main
building panel. Any insight will be appreciated. Thanks. I've also been told
that the NEC 2011 comments on 690.4 (B) clarify this. Can anyone comment?
Obviously I am not mixing DC and AC conductors.
Kirk Herander
Vermont Solar Engineering
802.863.1202
NABCEP(tm) Certified Solar Installer
NYSERDA-eligible Installer
VT Solar Incentive Program Partner
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________ List sponsored by Home Power magazine
List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org