Dan:

Just to be clear, I am not suggesting that Kirk draw anything. I suggest he refer to the drawing identified as Figure 690.1(B) in the 2008 NEC.

If the inspector will still not accept the facts, there is usually an appeal process.

I'm all for being polite, but I am also in favor of not letting an ignorant inspector take advantage of me or my clients.

William



At 05:50 AM 4/10/2011, you wrote:

William's suggestion for a clearly drawn one-line
is also excellent.

In the end, however, as we all know, it's the AHJ's
interpretation that prevails (right or wrong).


Dan


--- On Sun, 4/10/11, Kirk Herander, VSE <[email protected]> wrote:

> From: Kirk Herander, VSE <[email protected]>
> Subject: Re: [RE-wrenches] 690.4 (B) ???
> To: [email protected], "'RE-wrenches'"
> <[email protected]>
> Date: Sunday, April 10, 2011, 7:26 AM
> My situation does not concern AC and DC in the same
> raceway. It concerns an AC conductor from the utility
> main panel to a load subpanel, and a separate AC
> inverter output from an inverter combiner panel, back
> to the main panel, not being allowed in the same
> conduit - at least that's the interpretation
> of 690.4(B) of the 2008 NEC by my inspector.
>
> Kirk Herander
> Vermont Solar Engineering
> 802.863.1202
> NABCEP(tm) Certified Solar Installer
> NYSERDA-eligible Installer
> VT Solar Incentive Program Partner




_______________________________________________

William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to