Kirk:

When you say inverter combiner, I am confident you mean the device combining the AC output conductors of multiple inverters.

I got the same jive from an over zealous inspector once, but he and your inspector are just plain wrong. Examine and show them the diagram in the code book of PV source and output conductors (690.2). These are all DC PV conductors, not AC conductors, and, assuming the statement in the paragraph above is correct, the passage has no application here. This is a rookie inspector mistake.

Good luck,

William

PS: By saying the source and output connectors are connected together, this is an oblique way of describing the PV combiner, the one point where PV source and output circuits are connected together.

WM



At 06:10 PM 4/9/2011, Kirk Herander, VSE wrote:
2008 NEC states that:

(B) Conductors of Different Systems. Photovoltaic
source circuits and photovoltaic output circuits shall not be
contained in the same raceway, cable tray, cable, outlet box,
junction box, or similar fitting as feeders or branch circuits
of other systems, unless the conductors of the different systems
are separated by a partition or are connected together.

Can anyone describe and give an example of what "connected together" means
to inverter PV circuits in the same conduit as a branch (load) circuit?

I have a single existing PVC conduit to a barn with an AC load subpanel. I
want to run the output conductors of an inverter combiner panel in the barn
through the same conduit to get to be main building. The fill / derating
calcs work to do this. The inspector says I have to run a new conduit for
the AC inverter combiner because the subpanel feeder and the combiner output
conductors are "not connected". But they are both connected to the main
building panel. Any insight will be appreciated. Thanks. I've also been told
that the NEC 2011 comments on 690.4 (B) clarify this. Can anyone comment?
Obviously I am not mixing DC and AC conductors.



Kirk Herander

William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to