Connectors were fully engaged. I would also think what you described would 
cause an AC short, at least intermittently, in the connector. GFI tripping is a 
DC problem. It worked fine for 5 months until a week ago.

Kirk Herander
VSE

On Jun 17, 2011, at 12:27 PM, "Mark Frye" <[email protected]> wrote:

> I see.
>  
> My experience with the M190 ac connector is this: It is possible to join the 
> two connector halves and rotate the cuff sufficiently to establish an 
> electrical connection. But if you don't rotate the cuff until the detant is 
> engaged, you may not completely seal the connection by compressing the 
> internal face gasket.
>  
> I really haven't looked into it much further but I wonder if the water you 
> observed entered through an incomplete connector mate, along the conductors, 
> into the inverter enclosure?
> 
> Mark Frye 
> Berkeley Solar Electric Systems 
> 303 Redbud Way 
> Nevada City,  CA 95959 
> (530) 401-8024 
> www.berkeleysolar.com 
> 
>  
> 
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Kirk Herander
> Sent: Friday, June 17, 2011 4:51 AM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Enphase Nema 6 enclosure - not
> 
> yes
> 
>  
> 
> Kirk Herander
> 
> VT solar, LLC
> 
> dba Vermont Solar Engineering
> 
> NABCEPTM Certified installer Charter Member
> 
> NYSERDA-eligible Installer
> 
> VT RE Incentive Program Partner
> 
>  
> 
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Mark Frye
> Sent: Thursday, June 16, 2011 11:28 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Enphase Nema 6 enclosure - not
> 
>  
> 
> Was that an M190?
> 
> 
> Mark Frye 
> Berkeley Solar Electric Systems 
> 303 Redbud Way 
> Nevada City,  CA 95959 
> (530) 401-8024 
> www.berkeleysolar.com 
> 
>  
> 
>  
> 
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Kirk 
> Herander, VSE
> Sent: Thursday, June 16, 2011 6:50 PM
> To: 'RE-wrenches'
> Subject: [RE-wrenches] Enphase Nema 6 enclosure - not
> 
> I just figured out why I could not reset a GFI error on one of my 
> micro-inverters. First, I noticed condensation in the led lens, then water 
> literally dripped out of the AC side as soon as I disconnected it. This was 
> mounted on the top backside of a panel, roughly two ft above a flat roof. ….. 
> fascinating
> 
>  
> 
> Kirk Herander
> 
> Vermont Solar Engineering
> 
> 802.863.1202  fax 802.863.7908
> 
> VT RE Incentive Program  Partner
> 
> NYSERDA Incentive-eligible Partner
> 
> NABCEPTM    Certified Installer
> 
>  
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to