Larry,
I think you want the PWM controller to start first so the turn on will be 
smooth.  If the current capacity of the diversion controller is exceeded then 
you want the relay to switch in the big load.  At that point the diversion 
controller will back off and pickup the difference.  That is why I suggested 
the the relay controlled load be 50 to 75% of the pwm diversion load, so that 
whenever it turns on the pwm controller will be working, too.
David

David Katz
CTO & Founder
AEE Solar Inc
P: 707 825-1200
F: 707 825-1202
[email protected]
www.aeesolar.com
From: [email protected] 
[mailto:[email protected]] On Behalf Of Larry Crutcher, 
Starlight Solar Power Systems
Sent: Wednesday, November 30, 2011 8:49 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Diversion load for AC coupled system

David,
Ah..I think I see what you are saying. But, don't you mean .2 volts lower than 
the diversion load? That way there will only be limited current left for the 
diversion controller to handle. If it is the other way, what stops full current 
from flowing through the diversion controller if the .2 volts is not reached? 
Or is .2 volts two close to worry about that?