Larry,

I understand your point.
What I clarified is that periodic cycling is not a requirement or benefit in 
achieving longer flooded lead acid deep-cycle battery life. Equalization is 
still required depending application specific, yet at a much lower periodic 
rate than if the application was true cyclic.
I also agree that there are lead acid batteries out there designed just for 
floating applications. Their design focus on thinner plates for higher current 
and less cycling.  This technology does focus on low self-discharge, high 
corrosion resistance, not on the various technologies specifics related to deep 
cycling.  Hence they like floating applications that stays in float mode 99% of 
the time and need to crank power very occasionally. Cycling such batteries will 
be reducing dramatically their life.

In a nut shell: there are benefits to tap in both technologies. Certainly there 
are "UPS" applications where floating mode is not looking for deep-cycling. 
Certainly there are "cyclic" applications where deep-cycling capability are 
mandatory. And then you have all in between, which makes all of us excited with 
different opinions. Ask 10 battery experts and the answers will be "it 
depends". I would say, understanding the loads and the application is a great 
step towards long life. Next  steps are picking the right battery for the 
application, sizing, installation and maintenance.

John
John F. DeBoever
Global Technical Director - Renewable Energy
Trojan Battery Company

12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Skype: john.f.deboever
Fax: +1-562-236-3239
[email protected]<mailto:[email protected]>
www.trojanbattery.com<http://www.trojanbattery.com/>

From: [email protected] 
[mailto:[email protected]] On Behalf Of Larry Crutcher, 
Starlight Solar Power Systems
Sent: Thursday, February 16, 2012 11:30 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Interstate L-16 vs Trojan L-16REB

John,

Are you including your new RE battery as being acceptable for float/standby 
service without cycling? Since you do not recommend cycling your battery, do 
you also recommend no equalization charge when in float/standby use?

Frankly I question the logic of leaving any deep cycle flooded battery at a 
constant float voltage for months or years at a time. Do you have test data 
that will help me overcome my skepticism?

Thank you,

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103


On Feb 16, 2012, at 9:09 AM, John DeBoever wrote:


Wrenches,
Todd,

Trojan Battery manufactures only true deep-cycling lead-acid batteries, from 
our 4 factories, based in the USA.
Periodic cycling is not a requirement or benefit in achieving longer flooded 
lead acid deep-cycle battery life.

There are some valid reasons to prefer flooded lead-acid deep-cycle lead-acid 
batteries for some residential semi-cycling / semi-floating applications.  
Typical floating-only applications do not have to feature a true deep cycle, 
although our Trojan products will work fine, without requiring periodic 
cycling. There are some batteries being marketed and labeled Deep Cycle that 
are not, and these will be affected by any amount of cycling, which is giving 
the Lead Acid industry a not so good name.

John




This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to