Are you sure you can't? Since the bus has a rating of 150 A and is protected by a 100 A breaker, there is plenty of room to not over amp the bus from the two sources of power.

The amperage from the inverter will cancel amperage coming from the utility in the feeder. The wire will never supply over the 100 A. The theoretical max the inverter could backfeed would be 40 Amps in the 100 Amp cable if no loads were being supplied. It would certainly not be a safety issue. Am I missing something in the code?


At 12:51 AM 9/28/2012, you wrote:
Mac:

Nope.


William Miller

PS:  It's pretty straight forwards, the code says "bus or conductor."

wm

PPS:

Can you customer live with a smaller feeder breaker, say 125 amps? If so, your gold.

wm



At 06:43 PM 9/27/2012, you wrote:
Hello wrenches,

I am looking for advice on how the 120% rule applies to feeders for a subpanel. I have this scenario: 150A bus rating on subpanel with main breaker of 100A. The conductors feeding this subpanel are 100A rated conductors. Can I backfeed with a 40A breaker?

Thanks

--



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Internal Virus Database is out of date.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5272 - Release Date: 09/16/12 18:34:00

Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to