I agree.  With a 150A bus being fed by 100A from the grid leaves 80 additional 
amps (120% of 150A) to feed the bus from outside sources.  It seems to me that 
40A of PV being back fed will be just fine.  
  
Aaron Mandelkorn
NABCEP Certified PV Installer
Renewable Energy Outfitters
Box 65 Salida, CO. 81201
(970)596-3744
[email protected]
www.reosolar.com















On Sep 28, 2012, at 6:32 AM, Drake wrote:

> Are you sure you can't?  Since the bus has a rating of 150 A and is protected 
> by a 100 A breaker, there is plenty of room to not over amp the bus from the 
> two sources of power.
> 
> The amperage from the inverter will cancel amperage coming from the utility 
> in the feeder.  The wire will never supply over the 100 A.  The theoretical 
> max the inverter could backfeed would be 40 Amps in the 100 Amp cable if no 
> loads were being supplied.  It would certainly not be a safety issue.  Am I 
> missing something in the code?
> 
> 
> At 12:51 AM 9/28/2012, you wrote:
>> Mac:
>> 
>> Nope.
>> 
>> 
>> William Miller
>> 
>> PS:  It's pretty straight forwards, the code says "bus or conductor."
>> 
>> wm
>> 
>> PPS:
>> 
>> Can  you customer live with a smaller feeder breaker, say 125 amps?  If so, 
>> your gold.
>> 
>> wm
>> 
>> 
>> 
>> At 06:43 PM 9/27/2012, you wrote:
>>> Hello wrenches,
>>> 
>>> I am looking for advice on how the 120% rule applies to feeders for a 
>>> subpanel.  I have this scenario:
>>> 150A bus rating on subpanel with main breaker of 100A.  The conductors 
>>> feeding this subpanel are 100A rated conductors.  Can I backfeed with a 40A 
>>> breaker?
>>> 
>>> Thanks
>>> 
>>> -- 
>>> 
>>> 
>>> 
>>> Mac Lewis
>>> 
>>> "Yo solo sé que no sé nada." -Sócrates
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>>> Internal Virus Database is out of date.
>>> Checked by AVG - www.avg.com 
>>> Version: 8.5.455 / Virus Database: 271.1.1/5272 - Release Date: 09/16/12 
>>> 18:34:00
>> 
>> Miller Solar
>> Voice :805-438-5600
>> email: [email protected]
>> http://millersolar.com
>> License No. C-10-773985
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to