Mr. Brooks had an email on this topic on 5/8, 12:58pm ET. NEC officially
says that the conductor needs to be upsized but the 2014 will fix it
because that is dumb. I've copied some of Bill's email below.
**
The key distinction was used in my proposal to the 2014 NEC that removed
the statement “and conductor” in 705.12(D) since conductors are treated
very differently in the NEC. We in 690 are the ones that got this messed
up. The issue with conductors are taps. With two sources feeding a tap,
the sum of the feeder breakers would have to be taken into account in
sizing the tap. This does NOT mean that the tap is a full size
conductor. The tap rule determines the size and the new proposal simply
requires you to use both the feeder breaker and the PV breaker in sizing
the tap. This assumes that both breakers are feeding the tap in the
event of fault on the tap and that there would be no problem clearing
that fault. If fault current was used as an argument for oversizing (it
is wrong), it only has relevance in the tap scenario. A fault in a
feeder with no taps does not allow the sum of the currents to flow
anywhere but where the fault is—the rest of the conductor is undamaged
in a fault.
...
Sizing a conductor for the sum of two breakers on opposite ends of a
feeder seems to be what the code says, but it is totally ABSURD from a
technical point of view. John’s articles were merely pointing out that
the code language seems to be telling us to do this, regardless of
whether it makes technical sense. The 2014 NEC will do away with this
craziness.
**
On 2012/9/28 9:46, Kristopher Schmid wrote:
It seems to me that the conductor should not be subject to the 120% rule
despite what the code says. The potential safety issue here is
overloading the neutral bus, right? While feeding currents could be
additive in the panel, they would be subtractive on the feeder, no? I
seem to remember seeing this discussion on the list before.
Kris
On Fri, Sep 28, 2012 at 8:26 AM, Aaron Mandelkorn <[email protected]
<mailto:[email protected]>> wrote:
I agree. With a 150A bus being fed by 100A from the grid leaves 80
additional amps (120% of 150A) to feed the bus from outside sources.
It seems to me that 40A of PV being back fed will be just fine.
Aaron Mandelkorn
NABCEP Certified PV Installer
Renewable Energy Outfitters
Box 65 Salida, CO. 81201
(970)596-3744 <tel:%28970%29596-3744>
[email protected] <mailto:[email protected]>
www.reosolar.com <http://www.reosolar.com>
On Sep 28, 2012, at 6:32 AM, Drake wrote:
Are you sure you can't? Since the bus has a rating of 150 A and
is protected by a 100 A breaker, there is plenty of room to not
over amp the bus from the two sources of power.
The amperage from the inverter will cancel amperage coming from
the utility in the feeder. The wire will never supply over the
100 A. The theoretical max the inverter could backfeed would be
40 Amps in the 100 Amp cable if no loads were being supplied. It
would certainly not be a safety issue. Am I missing something in
the code?
At 12:51 AM 9/28/2012, you wrote:
Mac:
Nope.
William Miller
PS: It's pretty straight forwards, the code says "bus or conductor."
wm
PPS:
Can you customer live with a smaller feeder breaker, say 125
amps? If so, your gold.
wm
At 06:43 PM 9/27/2012, you wrote:
Hello wrenches,
I am looking for advice on how the 120% rule applies to feeders
for a subpanel. I have this scenario:
150A bus rating on subpanel with main breaker of 100A. The
conductors feeding this subpanel are 100A rated conductors. Can
I backfeed with a 40A breaker?
Thanks
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates
*
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
<mailto:[email protected]>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
Internal Virus Database is out of date.
Checked by AVG - www.avg.com <http://www.avg.com/>
Version: 8.5.455 / Virus Database: 271.1.1/5272 - Release Date:
09/16/12 18:34:00
Miller Solar
Voice :805-438-5600 <tel:805-438-5600>
email: [email protected] <mailto:[email protected]>
http://millersolar.com <http://millersolar.com/>
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
<mailto:[email protected]>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
<mailto:[email protected]>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
<mailto:[email protected]>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
Shine On!
Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
www.legacysolar.com <http://www.legacysolar.com/>
715-653-4295
NABCEP Certified PV Installer
BSEE
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org