Jason,
Glenn's point below sounds correct to me. We've run several microinverter projects with romex, but always have to do the transition in the attic because romex is not rated for wet locations. Some of the local jurisdictions around the Bay Area are onto this point. Also, NEC 250.64(B) deals with "securing and protection against physical damage" for the GEC. You're probably fine running a bare 6 or 4 AWG, but anything smaller than 6 AWG "shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor." So no bare 8 AWG allowed. I believe you can also use 4/3 romex which should have a #8 ground in it already but that might increase your wire cost. Best, August *From:* [email protected] [mailto: [email protected]] *On Behalf Of *Glenn Burt *Sent:* Thursday, October 25, 2012 8:37 AM *To:* 'RE-wrenches' *Subject:* Re: [RE-wrenches] Enphase and Romex Soladeck on the rooftop places it in an environment that is considered ‘wet’. I don’t think Romex is listed for use in a wet environment. This would force you to use the proposed jbox in the attic for the transition location. I also understood that you could combine the EGC and GEC into a single conductor as long as it is continuous or irreversibly spliced, as part of the ’08 code. -Glenn Burt *From:* [email protected] [ mailto:[email protected]<[email protected]>] *On Behalf Of *Jason Szumlanski *Sent:* Thursday, October 25, 2012 9:13 AM *To:* RE-wrenches *Subject:* [RE-wrenches] Enphase and Romex I'm sure this has been covered, but I could not find it in the archives. We are considering using Romex in the attic for the first time. My plan was to use the new Enphase coupler to connect the trunk cable to Type TC-ER, enter a Soladeck passthrough box on the roof into a junction box in the attic where I would make the transition to 10/3 Romex. I'm hung up on the GEC going back to the service panel. Any suggestions? By the way, we are on NEC 2008, and in most cases there is also a requirement for an additional grounding electrode per NEC 690.47(D) (that shouldn't really relate to my issue). *Jason Szumlanski** * *Fafco Solar*
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org