Hi Ryan,

There is a pin whole through each handle. If I connect the handles together 
with a pin, they can only be set or tripped as a set. So will this external 
"ganging" do the same thing? 

Thank you,

Larry Crutcher
Starlight Solar Power Systems



On Feb 27, 2013, at 9:44 AM, Ryan wrote:

Larry
Our 100 amp din rail is essentially 2 breakers in parallel. So in theory the 2 
60 amp breakers "Could" work but. My concern would be that they may not be 
tripped at the same time where they are not internally ganged. I can't say "Go 
Ahead" but.

Ryan
-- 
Ryan Stankevitz
Technical Support Manager
MidNite Solar Inc.
[email protected]
360-403-7207 XT 151
Skype ID ryan.midnite


On 2/27/2013 11:21 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
> We are installing the system today and I only have 60amp in stock. Customer 
> lives in CA and is leaving today after the installation.       
> 
> Larry Crutcher
> Starlight Solar Power Systems
> 
> 
> On Feb 27, 2013, at 9:17 AM, Jonathan Hill wrote:
> 
> Why not use one of Midnite's new 100 amp din breakers?
> 
> Jonathan Hill
> Solar applications engineer
> Solar Electric Supply
> 530-559-3781
> [email protected]
> 
> 
> On Feb 27, 2013, at 8:06 AM, "Larry Crutcher, Starlight Solar Power 
> Systems"<[email protected]> wrote:
> 
>> Hello Wrenches,
>> 
>> I am installing a Classic 150 controller in an RV with potential 95 amps 
>> output at 12 volts. The customer has a Midnite DIN box and wants me to use 
>> it for the controller output. I am out of 150VDC breakers but I have two 60 
>> amp breakers. Is it safe and reliable to use the 2 breakers in parallel for 
>> this purpose? I can pin the two handles together. There will be other 
>> circuit protection at the battery.
>> 
>> Thank you,
>> 
>> Larry Crutcher
>> Starlight Solar Power Systems
> 
> 


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to