Larry:
I was tempted to advise against this. I see a similar concept with people
trying to parallel PV feeds and then putting two charge controllers at the
destination. Not good.
However, I see many 200 amp main breakers that are 4 100 amp breakers
ganged, with two for each phase. I can not presume to know about the
requirements of internal ganging.
William Miller
At 08:06 AM 2/27/2013, you wrote:
Hello Wrenches,
I am installing a Classic 150 controller in an RV with potential 95 amps
output at 12 volts. The customer has a Midnite DIN box and wants me to use
it for the controller output. I am out of 150VDC breakers but I have two
60 amp breakers. Is it safe and reliable to use the 2 breakers in parallel
for this purpose? I can pin the two handles together. There will be other
circuit protection at the battery.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5635 - Release Date: 02/26/13
17:46:00
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org