Larry:

I was tempted to advise against this. I see a similar concept with people trying to parallel PV feeds and then putting two charge controllers at the destination. Not good.

However, I see many 200 amp main breakers that are 4 100 amp breakers ganged, with two for each phase. I can not presume to know about the requirements of internal ganging.

William Miller



At 08:06 AM 2/27/2013, you wrote:
Hello Wrenches,

I am installing a Classic 150 controller in an RV with potential 95 amps output at 12 volts. The customer has a Midnite DIN box and wants me to use it for the controller output. I am out of 150VDC breakers but I have two 60 amp breakers. Is it safe and reliable to use the 2 breakers in parallel for this purpose? I can pin the two handles together. There will be other circuit protection at the battery.

Thank you,

Larry Crutcher
Starlight Solar Power Systems





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5635 - Release Date: 02/26/13 17:46:00

Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to