Good point Ross. The panel is marked as a 200A with no indication that the bus has a higher rating, so I've assumed 200A. I considered downsizing the MB, but it's an discontinued panel, and filled to capacity so not exactly ideal.
Thanks, Garrison ________________________________ From: [email protected] [[email protected]] on behalf of Ross Taylor [[email protected]] Sent: Thursday, February 28, 2013 9:24 PM To: [email protected] Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection Hi Garrison, This is a great discussion and I think I've read all the responses. If I missed this question, please forgive me. But, in your original post you refer to a 200 amp service. I don't, though, see mention of the rating of the bus bars. The bus bars may be rated for something more than 200 amps, depending upon the panel, even if they're protected by a 200 amp main disconnect. If so, that would increase your backfeed breaker sizing options. Best wishes, Ross Taylor
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org