Good point Ross.  The panel is marked as a 200A with no indication that the bus 
has a higher rating, so I've assumed 200A.  I considered downsizing the MB, but 
it's an discontinued panel, and filled to capacity so not exactly ideal.

Thanks,

Garrison
________________________________
From: [email protected] 
[[email protected]] on behalf of Ross Taylor 
[[email protected]]
Sent: Thursday, February 28, 2013 9:24 PM
To: [email protected]
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

Hi Garrison,

This is a great discussion and I think I've read all the responses. If I missed 
this question, please forgive me.  But, in your original post you refer to a 
200 amp service.  I don't, though, see mention of the rating of the bus bars.  
The bus bars may be rated for something more than 200 amps, depending upon the 
panel, even if they're protected by a 200 amp main disconnect.  If so, that 
would increase your backfeed breaker sizing options.

Best wishes,

Ross Taylor