I've got a question about battery string fusing. Typically we size the wire from the batteries to the inverter based on continuous rating procedures (max power/efficiency)*125%.
However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the source current. That is no big deal for the wire, because it is a short time frame... little heat will be generated. However, in fusing the sub-strings, you need to account for that peak surge current so you don't blow fuses all the time. But if you put a 500-1000 amp fuse on a 4/0 wire, above the max surge draw of the inverter, the wire will be under-protected for its ampacity rating. Any thoughts on the catch-22? thanks, Troy Harvey --------------------- Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org