I've got a question about battery string fusing. Typically we size the wire 
from the batteries to the inverter based on continuous rating procedures (max 
power/efficiency)*125%. 

However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the source 
current. That is no big deal for the wire, because it is a short time frame... 
little heat will be generated. However, in fusing the sub-strings, you need to 
account for that peak surge current so you don't blow fuses all the time. But 
if you put a 500-1000 amp fuse on a 4/0 wire, above the max surge draw of the 
inverter, the wire will be under-protected for its ampacity rating. Any 
thoughts on the catch-22?