I just finished a rewire and we kept the Ananda power center, Allan :-)
Back when we used class T fuses more they were always over sized relative to Heinemann breakers.
400 amp class T fuse = 250 amp breaker= 4/0 cable
200 amp class T fuse = 175 amp breaker= 2/0 cable

I still think class T fuses are superior in some ways to breakers: they have better interrupt capacity and trip faster in a short circuit condition.

However, If you spend too much time thinking about and looking at the trip curves, you'll break your brain and special order some weird fuses and breakers. (anybody need a 350 amp class T fuse?) Just follow the inverter manufacturer's recommendations and all will be well. On the other hand, William has brought up a topic I have harped on for years: Having the OCPD in the cabinet doesn't protect the majority of the circuit. Class T fuses at the battery terminals do, but they're not rated for the corrosive environment. I have thrown a few class T fuses away that had acid eating away at the ends. I don't have the solution, but I will continue to point out that this is a real problem. Dropping a wrench across the battery terminals can lead to a spectacular failure that not only can cause a fire, but might even cause a battery explosion, yet NEC offers no protection.
We use insulated wrenches from experience, and hope for the best.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/5/2013 8:29 PM, William Miller wrote:
Friends:

Good topic.  Some questions:

1. Most manufacturer's present an installation guide that shows one OCPD in the battery circuit and that is in the BOS cabinet. This means the battery leads are unprotected. Do we need an OPCD at the battery terminals?

2. Class T fuses are generally recommended for this application. The data shows them as "fast acting." Is this a problem? Will they act too fast and open during normal surge loads?

Thanks in advance!

William Miller





Troy,

Overcurrent device size is matched to the conductor size. The inverse time constant nature of an overcurrent device can typically handle the surge currents as long as conductor sizing has truly been done correctly for the conductor. Circuit breakers are preferred to fuses because they can be reset.

There has been volumes written on this issue. The constant current at lowest battery voltage should be used, plus the ac ripple content on the battery circuit. This is usually a much larger conductor than your average designer will plan for. The best thing is to look at Midnight, Outback, and Schneider and see what size overcurrent devices they require for their products. That will give you a good clue as to how to size the conductor and overcurrent device.

Bill.

*From:* [email protected] [mailto:[email protected]] *On Behalf Of *Troy Harvey
*Sent:* Friday, April 05, 2013 3:38 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Fuse sizing in battery circuits

I've got a question about battery string fusing. Typically we size the wire from the batteries to the inverter based on continuous rating procedures (max power/efficiency)*125%.

However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the source current. That is no big deal for the wire, because it is a short time frame... little heat will be generated. However, in fusing the sub-strings, you need to account for that peak surge current so you don't blow fuses all the time. But if you put a 500-1000 amp fuse on a 4/0 wire, above the max surge draw of the inverter, the wire will be under-protected for its ampacity rating. Any thoughts on the catch-22?


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to