Phil,

Thanks for the code references, they are very useful and point out an area where I fear many installations of battery based inverters are deficient. You are right the manufacturers have not made this easy!

First, data on the short circuit current available from most batteries isn't easily available, if available at all. Concorde publishes short circuit current numbers for the SunExtender batteries. Neither Trojan, Rolls/Surrette, nor Outback publishes short circuit current data for their batteries. Full River publishes an internal resistance number that can be used to estimate the short circuit current. Taken as a whole, battery manufacturer's certainly haven't made it easy to comply with 690.71

Second, sometimes interrupting capacity data on the breakers being used in BOS equipment is also missing. Take a look at Outback's catalog and try to find the AIC for the breakers used to protect the inverter wiring. Is it published anywhere else? Should a system designer have to buy the Outback breaker, find out who manufactured it, and then search for the correct ratings in the in the breaker manufacturer's catalog? Obviously not.

Third, BOS manufacturers often connect circuit breakers for charge controllers or dc utilization circuits that have AIC ratings of only 5000 amps directly to the battery. So while the inverter may be protected with a breaker having an AIC rating 25,000 or 50,000, other devices don't. BOS manufacturer's should include on the dc breaker panel data showing the lowest AIC breaker that is connected directly to the battery. Then installers would have at least half of the information needed to decide when a fuse is needed to backup the dc breakers. And shouldn't the instructions for BOS equipment point out that a fuse may be necessary at the battery.

The short circuit current from a single string of golf cart batteries or L16 batteries is probably less than 5000 amps. Fuse(s) are probably needed in most installations with larger batteries or battery systems with multiple strings of batteries. 2011 NEC 240.21(H) allows overcurrent protection to be installed as close as practical to battery terminals - even in classified locations.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com


On 4/6/2013 7:29 AM, Phil Undercuffler wrote:
Ray,

690 does offer the protection, it's just that most maufacturers haven't made it easy.

690.71 Installation

(C) Current Limiting. A listed, current-limiting, overcurrent device shall be installed in each circuit adjacent to the batteries where the available short-circuit current from a battery or battery bank exceeds the interrupting or withstand ratings of other equipment in that circuit. The installation of current-limiting fuses shall comply with 690.16.


The telcom industry has been doing this for years. Their norm is to have each string of batteries on a shelf, and terminate at a breaker. Each string then is combined at a bus bar or plate, to help ensure equal current on each string. The loads and charging sources all come to that same bus bar. It has some advantages, as individual strings can be monitored and serviced without taking the entire system down.

FWIW, OutBack makes a battery rack for AGM batteries with series string overcurrent and disconnects on every string. It's also to my knowledge the first UL1741 Listed device available -- the other stuff I've seen is either not listed, or is trading on old 508a standards. AGMs might not be for every installation, but for jobs where they are appropriate this could be a good, code-compliant solution.


Phil Undercuffler
OutBack Power




On Friday, April 5, 2013, Ray Walters wrote:

    I just finished a rewire and we kept the Ananda power center,
    Allan :-)
    Back when we used class T fuses more they were always over sized
    relative to Heinemann breakers.
    400 amp class T fuse = 250 amp breaker= 4/0 cable
    200 amp class T fuse = 175 amp breaker= 2/0 cable

    I still think class T fuses are superior in some ways to breakers:
    they have better interrupt capacity and trip faster in a short
    circuit condition.

    However, If you spend too much time thinking about and looking at
    the trip curves, you'll break your brain and special order some
    weird fuses and breakers.  (anybody need a 350 amp class T fuse?)
     Just follow the inverter manufacturer's recommendations and all
    will be well.
    On the other hand, William has brought up a topic I have harped on
    for years:  Having the OCPD in the cabinet doesn't protect the
    majority of the circuit.  Class T fuses at the battery terminals
    do, but they're not rated for the corrosive environment.  I have
    thrown a few class T fuses away that had acid eating away at the ends.
    I don't have the solution, but I will continue to point out that
    this is a real problem. Dropping a wrench across the battery
    terminals can lead to a spectacular failure that not only can
    cause a fire, but might even cause a battery explosion, yet NEC
    offers no protection.
    We use insulated wrenches from experience, and hope for the best.

    R.Ray Walters
    CTO, Solarray, Inc
    Nabcep Certified PV Installer,
    Licensed Master Electrician
    Solar Design Engineer
    303 505-8760

    On 4/5/2013 8:29 PM, William Miller wrote:
    Friends:

    Good topic.  Some questions:

    1. Most manufacturer's present an installation guide that shows
one OCPD in the battery circuit and that is in the BOS cabinet. This means the battery leads are unprotected. Do we need an OPCD
    at the battery terminals?

2. Class T fuses are generally recommended for this application. The data shows them as "fast acting." Is this a problem? Will
    they act too fast and open during normal surge loads?

    Thanks in advance!

    William Miller





    Troy,

    Overcurrent device size is matched to the conductor size. The
    inverse time constant nature of an overcurrent device can
    typically handle the surge currents as long as conductor sizing
    has truly been done correctly for the conductor. Circuit
    breakers are preferred to fuses because they can be reset.

    There has been volumes written on this issue. The constant
    current at lowest battery voltage should be used, plus the ac
    ripple content on the battery circuit. This is usually a much
    larger conductor than your average designer will plan for. The
    best thing is to look at Midnight, Outback, and Schneider and
    see what size overcurrent devices they require for their
    products. That will give you a good clue as to how to size the
    conductor and overcurrent device.

    Bill.

    *From:* [email protected]
    <javascript:_e({}, 'cvml',
    '[email protected]');>
    [mailto:[email protected]
    <javascript:_e({}, 'cvml',
    '[email protected]');>] *On Behalf Of
    *Troy Harvey
    *Sent:* Friday, April 05, 2013 3:38 PM
    *To:* RE-wrenches
    *Subject:* [RE-wrenches] Fuse sizing in battery circuits

    I've got a question about battery string fusing. Typically we
    size the wire from the batteries to the inverter based on
    continuous rating procedures (max power/efficiency)*125%.

    However a 6kW inverter, can peak at 12kW for 5-10 seconds,
    doubling the source current. That is no big deal for the wire,
    because it is a short time frame... little heat will be
    generated. However, in fusing the sub-strings, you need to
    account for that peak surge current so you don't blow fuses all
    the time. But if you put a 500-1000 amp fuse on a 4/0 wire,
    above the max surge draw of the inverter, the wire will be
    under-protected for its ampacity rating. Any thoughts on the
    catch-22?


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to