Dan,
I think this thread applied not to OCDs but to an unfused 600VDC disconnect can
mounted on a roof which is less than vertical.
Bob-O
On Nov 11, 2013, at 9:21 AM, Exeltech wrote:
Wrenches,
There appears to be some misinformation getting into this thread.
The "trip" mechanism within standard thermal over-current protective devices
("OCP devices") is mechanically spring-loaded, and is triggered by heat.
Eric mentions below that Square D breakers are tested in a vertical orientation
only - the implication being that's their only "UL certified" position. If
this were true, it would imply the breakers cannot be used in any other
orientation. This would potentially limit the Square D OCP market to
sub-panels and other enclosures where the devices are vertical. Inasmuch as
the vast majority of panelboards I've encountered in my 40+ years in this
industry have the breakers stacked horizontally, it would not be a wise
business decision for the manufacturer to self-inflict such a limitation on
their product.
This also does not mean any such limitation (real or not) applies to all
breakers.
By way of example, OCP devices work in a horizontal position, stacked "pancake"
style in a main panelboard, as well as vertically oriented side-by-side in a
sub-panel. In either orientation, they are in full compliance with UL 489,
(UL Standard for Circuit Breakers, Switches, and Circuit Breaker Enclosures).
If an OCP device *was* positionally-sensitive, UL Standards require this
sensitivity to be noted in the documentation accompanying the device. Further
to that point, UL 489 Section 7.1.1.13 states: "In determining if a circuit
breaker complies with the test requirements, the device shall be mounted or
supported as in service and tested under conditions approximating those of
intended operation, except as otherwise noted."
Mounting position notwithstanding, a greater concern would be the ambient
temperature of a rooftop location, whereby summer heat would tend to make the
OCP device more sensitive than necessary, potentially causing it to trip at an
amperage below that of its UL ratings. While a nuisance, a more serious issue
arises when operating the OCP device in cold ambient conditions, whereby the
device may allow MORE than its rated trip current to flow.
Per UL 489, OCP devices are tested at either 25C or 40C ambient. Again per UL
489, if an OCP device is to be used in ambient conditions other than those two
ranges, the acceptable temperature range for that OCP device shall be marked on
the body of the device.
In UL 489, Supplemental Annex, Section 2, Subsection 2.3.3, mechanical
vibration testing is conducted with OCP devices oriented vertically,
horizontally, and inclined 30 degrees from vertical, with all devices energized
up to 200% of the device rated current during the testing.
Given the preceding, and per implication of UL 489 testing methods, OCP devices
are NOT positionally sensitive.
In conclusion, if you DO install a rooftop OCP system, and for proper
protection, please ensure the OCP devices utilized are rated for the worst-case
ambient temperatures involved.
Regards to all,
Dan Lepinski
At 09:33 AM 11/8/2013, you wrote:
Hi Kirpal,
All Square D safety switches are UL tested in the Vertical position ONLY, so if
someone is trying to install a switch in any other position other than
vertical, that will be between them and the inspector.
Hope this helps.
Eric
____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES |
Technical Support Representative
Phone: +(650) 351-8237 ext. 001# | Email:
[email protected] | Site: www.schneider-electric.com/solar
| Address: 250 South Vasco Rd., Livermore, CA 94551
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org