William,
If your Vmp drop is under 2% (my design goal for maximum acceptable loss) I 
can't see any reason why not.

Larry 





On Dec 17, 2013, at 3:00 PM, "William Miller" <[email protected]> wrote:

Friends:
 
I am reworking an existing off-grid system to become a grid-tie with 
micro-inverters.  With your help, we have already determined that the M-190 
inverters will work and we have acquired the 9 of them we need.
 
Since the installation was completed in 1996, the home owner has installed a 
shade cover over a skylight.  Some of the supporting structure is preventing us 
from getting under the modules to install the M-190s.  Each module was fed to 
the equipment cabinet since the combiner was located there.  I have decided it 
will be much easier to install the M-190s in the equipment cabinet.  We have 
everything we need there:  The individual PV leads (in 10AWG), the breaker 
panel and room to mount the inverters.  Can any of you see any reason why the 
M-190s can’t be installed no on the roof?
 
Thanks in advance,
 
William
 
 
 
 
<image002.jpg>
17395 Oak Rd. Atascadero, CA 93422
www.millersolar.com
805-438-5600 voice
 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to