Eric:

Check which code version your AHJ is using. Earlier versions calculated solely 
on OCPD ratings. CA building codes are based on NEC 2008 for 11 more days, then 
2011. 

William 


> On Dec 19, 2013, at 4:03 PM, "SunHarvest" <[email protected]> wrote:
> 
> Sounds like I may be misinterpreting something but I don't think so...
>  
> NFPA 70, 2014 NEC 705.12(D2)(3)(b) states, "The sum of 125% of the 
> inverter(s) output circuit current and the rating of the overcurrent device 
> protecting the busbar shall not exceed 120% of the ampacity of the busbar."
>  
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to