Thanks for the reply and article, August. John Wiles's article makes a
clear statement that the GEC is not required for TL inverters. I wish the
code would say it that clearly! I think I'm going to have a tough time
convincing inspectors the GEC isn't required with such unclear language in
the code. We'll see....

Thanks again!

Dana

Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com
[email protected]
360.318.7646

On Mon, Nov 3, 2014 at 12:45 PM, August Goers <[email protected]> wrote:

> Hi Dana,
>
>
>
> This is still a confusing issue, I agree. This article helps a bit:
>
>
>
> http://www.nmsu.edu/~tdi/pdf-resources/IAEI%20Mar_Apr%202012.pdf
>
>
>
> If you look in a SMA TL inverter installation manual, for example, they
> only mention equipment grounds – there is no reference to a GEC that I can
> find. The 2014 code doesn’t seem to have clear wording on not requiring a
> GEC to me but Rebekah’s recap below is spot on. Luckily it is widely
> accepted in our neck of the woods that TL inverters don’t need GECs.
>
>
>
> I’m not familiar with the Solectria TL product. It sounds like it will be
> best to call them if you need to install one of their inverters.
>
>
>
> Best,
>
>
>
> August
>
>
>
> *From:* RE-wrenches [mailto:[email protected]] *On
> Behalf Of *Dana Brandt
> *Sent:* Monday, November 03, 2014 12:06 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Code reference request
>
>
>
> I think I'm a bit confused on this point. I can't seem to find the code
> that specifically exempts the GEC requirement for inverters of ungrounded
> PV systems. The only exception I can find is only for AC PV modules (2014
> NEC 690.47 (C) ).
>
> I just looked in the installation manual for Solectria's new TL inverters
> and found this:
> "Per NEC 690.47, a GEC must be installed, and the Grounding Electrode
> Terminal (GET) conductor must be sized in accordance with NEC article
> 250.166."
>
> What am I missing?
>
> Thanks,
>
>
> Dana
>
> Dana Brandt
> Ecotech Energy Systems, LLC
> www.ecotechenergy.com
> [email protected]
> 360.318.7646
>
>
>
> On Tue, Oct 28, 2014 at 11:30 AM, Rebekah Hren <
> [email protected]> wrote:
>
> If you are on 2014:
>
>  690.47(B)
>
> An ac equipment grounding system shall be permitted
>
> to be used for equipment grounding of inverters and other
>
> equipment *and for the ground-fault detection reference for *
>
> *ungrounded PV systems.*
>
>
>
> and 690.47(C)(3)
>
> *For ungrounded systems, this conductor shall be sized in accordance with
> 250.122 *and shall
>
> not be required to be larger than the largest ungrounded
>
> phase conductor.
>
>
>
> On Tue, Oct 28, 2014 at 2:22 PM, Gary Willett <
> [email protected]> wrote:
>
> Kirk:
>
> A DC grounding electrode conductor (GEC) is not required for inverters
> that do NOT have a ground reference for the PV+ and PV- conductor(s) from
> the PV array.
>
> A GEC is not required if the string inverter is one of the new TL
> (transformerless) types.  Also, this applies to micro-inverters such as the
> new Enphase M250 and later versions of the M215.
>
> Where this applies, only a properly sized equipment grounding conductor
> (EGC) is required.
>
> The EGC is sized according to [NEC 690.45] and can be a minimum of #14AWG
> when not exposed to damage, or #6AWG when exposed to potential damage.
>
> Regards,
>
> Gary Willett PE
> Icarus Engineering LLC
>
>
>
> On 10/28/14, 12:53 PM, Kirk wrote:
>
> Hi,
> I'm on a jobsite without my code book. Could someone tell me where in the
> code ungrounded systems do not require the inverter GEC? Basically my
> onsite electrician doesn't believe me. Thanks.
>
> Kirk Herander
> VSE
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
>
> --
>
> Tel: 336.266.8800
> http://o2energies.com/
> Project Engineer
> NABCEP Certified PV Installation Professional™ 091209-85
> NC Licensed Electrical Contractor
>
> This message, together with any attachments, is intended only for the
> named recipient(s).   It may contain confidential or privileged information
> that may be exempt from disclosure under applicable law.  If you are not
> the intended recipient(s), you are notified that the disclosure,
> dissemination, distribution, copying, storing, or other use of the contents
> of this message or its attachments is strictly prohibited.  If you receive
> this message in error, or are not the named recipient(s), please notify the
> sender at either the email address or telephone number above and delete
> this email from your computer.  Thank you.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to