To add; I am a firm believer that every few years I will send OB CC/Mates in 
for firmware up date. I will repole an off grid system at least twice a year. 
Temp sensor is imperative! and if the site is not maned do not set auto eq.
On Nov 18, 2014, at 1:40 PM, Allan Sindelar wrote:

> Drake,
> I'll add just a bit to Jarmo's excellent reply:
> You mentioned that you were unsure if the MX60 was set to auto-EQ. This could 
> be a source of trouble. The MX60 had the unfortunate characteristic whereby 
> if set to auto-EQ, it would continue to try to complete an EQ indefinitely 
> once triggered. As such, if the array was not sufficient to hold the 
> batteries above the EQ voltage for the set duration, or as the batteries aged 
> and their internal resistance increased such that the EQ voltage couldn't be 
> maintained, the controller would never complete and exit EQ mode. 31V, while 
> conservative, is high enough to cause this.
> 
> If that is what occurred here, then disabling automatic EQ and reducing the 
> EQ voltage below gassing threshold should prevent recurrence.
> Allan
> 
> Allan Sindelar
> [email protected]
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
> On 11/18/2014 11:03 AM, [email protected] wrote:
>> Hi: 
>> 
>> This may not be the problem, but I wanted to bring it up as I have heard of 
>> a few cases of battery boiling issues with various charge controllers and 
>> want to suggest a possible cause. 
>> 
>> I'll do this point form.  It's easier to describe it that way: 
>> 
>> 1. Solar charge controllers are programmed to go to bulk charge in the 
>> morning. 
>> 2. The intensity of the sunlight starts off low in the morning and depending 
>> on the weather during the day, the intensity can reach any level between 
>> virtually 0% and 100%. 
>> 3. The exit criteria for bulk is that the battery voltage reaches the 
>> Vbulk/abs volts setting or a bulk/abs timer times out. 
>> 4. If the sunlight conditions are just right to keep the charging voltage 
>> just below the Vbulk/abs setpoint, the exit from bulk/abs will be the timer. 
>> 5. Bulk/Abs timers are usually set for rather a long time, many hours is not 
>> uncommon. 
>> 6. Given the above, it is possible that the battery stays at gassing 
>> voltages for many hours every day at certain times of the year when the 
>> sunlight intensity is just right to support that. 
>> 7. As a consequence the boiling problem will show up only at particular 
>> sites, particular battery/charge controller sizes and particular times of 
>> year. 
>> 
>> Again, I am not suggesting that this is necessarily the cause of battery 
>> "boiling" in systems with solar charge controllers, but it could be a 
>> reason. 
>> 
>> 2nd ps.  All manufacturers do precise battery voltage/current measurements 
>> on the bench with a wide variety of conditions, but we will never be able to 
>> simulate the 1000's of conditions that happen on the 1000's of installs out 
>> there.  With that in mind, on-site battery voltage/current data logging is a 
>> very powerful tool when investigating these kinds of issues. 
>> 
>> JARMO
>> _____________________________________________________________________________________
>>  
>> 
>> Jarmo Venalainen  |   Schneider Electric   |  Solar Business  |   CANADA  |  
>>  Training & Development Specialist - Senior 
>> Phone: +604-422-2528  |   Fax: +604-420-1591  |   Mobile: +604-505-0291 
>> Email: [email protected]  |   Site: www.SEsolar.com  | 
>>   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
>> 
>> <Mail Attachment.jpeg>
>> *** Please consider the environment before printing this e-mail 
>> 
>> 
>> 
>> From:        Drake <[email protected]>
>> To:  RE-wrenches <[email protected]>,
>> Date:        11/18/2014 09:15 AM
>> Subject:     [RE-wrenches] Suspect MX 60
>> Sent by:     "RE-wrenches" <[email protected]>
>> 
>> 
>> 
>> Hello Wrenches,
>> 
>> An MX 60 boiled a 24 volt bank of 4 Trojan L-16 batteries last summer. The 
>> batteries all checked out to be in good shape. It is not totally clear that 
>> the CC was not set to auto equalize, but the EQ voltage was only set at 31.0 
>> V. 
>> 
>> The battery bank has been replaced by 8 Full River L-16 AGM batteries. The 
>> parameters have all been reset for AGM with EQ disabled. The homeowners are 
>> concerned that the charge control may not work, and damage their new battery 
>> bank. 
>> 
>> If there is a problem with the CC, it is very intermittent. Has anyone ever 
>> seen an intermittent MX 60? 
>> 
>> Outback tech support says if we send it in they will update the firmware for 
>> $90, and do a 24 hour bench test. It appears that the firmware update will 
>> not do anything useful for this off grid system. There are no new boards 
>> available for this unit. I'm not sure if the bench test will show up an 
>> intermittent problem. 
>> 
>> Has anyone had this situation before?  Would it be better to:
>> Replace the CC
>> Send the CC to Outback
>> Do nothing
>> Thank you,
>> 
>> Drake 
>> 
>> Drake Chamberlin
>> Athens Electric LLC
>> OH License 44810
>> CO License 3773
>> NABCEP Certified Solar PV 
>> 740-448-7328
>> http://athens-electric.com/ 
>> 
>> 
>> 
>> ______________________________________________________________________
>> This email has been scanned by the Symantec Email Security.cloud service.
>> _____________________________________________________________________________________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> [email protected]               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to