The minimum conductor size that can be paralleled, according to the NEC is
1/0.



William C. Turberville P.E.

President

Electrical Contracting Enterprises LLC

3080 Stage Post Dr ste 107

Bartlett, TN 38133

901-348-9230 ext 101 phone

901-289-6346 cell

901-348-2192 FAX







*From:* RE-wrenches [mailto:[email protected]] *On
Behalf Of *Jerry Shafer
*Sent:* Tuesday, December 02, 2014 11:45 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Parallel Wire combining



We have installed multible mcm 500 to meet this and there were three on
each leg but that was because of the required size and bending room
Jerry

On Dec 2, 2014 7:43 AM, "Larry" <[email protected]> wrote:

Wrenches,

If I combine 3 conductors of equal length in parallel, is the resulting
size equal to 3 times the Circular Mil area? For example, #4 is 42,080cm so
are three #4's close to 2/0 (134,200cm) in size? Is it as simple as this?
Assuming the conductors can not be removed individually, does this mean the
current capacity is equal to the resulting wire size?

Thanks, Larry
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to