That's the part that is throwing me off. If I have 3 times the circular
mil and compare that to a single conductor of similar circular mil, how
do I have 3 times the ampacity? These are very different numbers.
Example: 1/0 @ 90c is 170 amps x 3 = 510 amps. 510A is what a conductor
just over 750 AWG will carry. The circular mils of 3 1/0 cables is only
325,050 or a 325 AWG cable which would be rated at about 330 amps.
So, is it 510 amps (3x the ampacity) or 330 amps (3x circular mil)? And,
more importantly, why?
Larry
On 12/2/14 11:14 AM, Bill Turberville wrote:
I am sorry. Bad fingers. Three times the ampacity under the same