Hey boB,

This is the reference table I was using. They show 325 AWG and 325kCM refer to the same diameter cable but I should have used kcm for clarity.

If all insulation/temp rating is the same we are back to my original question. Anyone else able to explain this? To be safe I am leaning toward using the combined CM number to size for current rather than 3 times the ampacity as that just makes no sense to me.


On 12/2/14 3:54 PM, [email protected] wrote:

The "area" of the conductor will be 3 times and you would think that the NEC Ampacity would also be 3 times that of one conductor. But one LARGE conductor with the same area might not be as high as you think because of insulation. I would think that ampacity of 3 cables in parallel would be 3 times. But probably not when you take a single cable of the 3X area out of the NEC table. (I haven't looked at this to verify)

Also, Larry, 325 AWG 750 AWG (gauge) wire is a bit too small for this, don't you think ?

I know...  You mean circular mils...
boB




_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org