Wrenches,
We have issues with a 1-1/2 year old 25 kW grid-tied PV system utilizing 2 step 
up transformers from the array to grid. Actually it’s two identical, 12.5 kW 
systems (for incentive and financing reasons) on each transformer. Note that 
the inverter size and voltage selection was also dictated by incentives. Each 
of the two systems are designed as follows:

- 3, 3.8 kW, 240 Vac inverters (16A max output current) across each phase of 
the 240V, 3-ph Delta primary of a 15 kVA transformer. Each inverter 1-ph output 
has a fused disconnect. The output of all three inverters is combined into 3 
phase delta configuration with terminal blocks before the transformer. Other 
than the inverter AC disconnects there is no OCPD on the 3-ph primary side of 
the transformer.

- Transformer secondary to grid is 277/480 wye. The secondary output has two 
fused disconnects (one at each end of the 600-ft run between array and 
line-side connection) each with 20-A fuses.

After more than year of operation we noticed one inverter, in one of the two 
identical systems, was down (monitoring showed it happened past December), 
indicating a grid problem. One fuse (of the 3) in the secondary (grid-side) 
fused disco had blown. Replaced that fuse, but then 2 fuses at the disconnect 
near the meter, 600 feet away, popped. 

Systematic checking of the system reveals no shorted conductors, but a problem 
at the transformer. Close inspection revealed that the insulation on our 90˚C 
neutral conductor had slightly melted where it touched the X-O neutral wire of 
the transformer (the splice looked fine). Now it gets more interesting….

In the last week, while troubleshooting the first 12.5 kW system, its adjacent 
twin system had an inverter quit with a ground-fault error (these inverters 
commonly will display ground fault errors for other reasons). One of the 20A 
fuses in the secondary (grid 277/480) side had popped. And, yup, the neutral 
wire had signs of overheating. We shut all three inverters down in that system. 
The transformer doesn’t seem damaged, hopefully because we caught it in time. 
But we’re looking at a replacement transformer for the first system.

Here’s what we think may have happened: The grid went down and, on coming back 
on, the in-rush current to the secondary side of the transformer popped a 
(undersized) fuse, taking out one leg of the 480. One inverter on the primary 
side saw a bad grid and dropped out, but the other two connected and kept 
producing. This unbalanced production resulted in the neutral of the secondary 
wye (grid) side of the transformer, being overloaded. Over 3 months this 
unbalanced operation damaged the transformer.

Initially we replaced the fuses near the line-connection with 60A (it’s a 
hot-swap and we don’t want those to go again unless the conductors need it), 
and the fuses near the array transformer secondary with 30A, thinking that will 
handle the inrush current to the transformer after a grid outage better than 
the 20A fuses. However, after a lot of discussion, research, and consideration 
of the risk (of replacing another transformer) we’re wondering if we need to 
alter the design more substantially. 

The main design change we’re considering is to replace the fused disconnect on 
the secondary side with a 3-phase breaker, that will shut off all phases of the 
grid supply simultaneously in case of an over-current fault. But, what if one 
inverter just plain quits and that breaker stays on? Will the neutral on the 
secondary still be overloaded from the other two?
Other changes we’re pondering include:
- Do we need a ganged 3-ph breaker on the inverter side, so that all three 
inverters go off at once? This will only be useful in case of over current on 
an inverter output, which isn’t likely, and is now addressed with the fused 240 
AC 1-ph disconnects on the inverter outputs.
- Use a step-down transformer in reverse. I.E. use a 277/480 wye primary and 
240 delta secondary and back feed the secondary with the PV. Some info from 
other sources suggest that this will reduce the inrush current from the grid 
after an outage. I think this would be inefficient at transmitting the PV power.
- Can/should we remove the neutral connection to the transformer on the 
secondary side? There are no 277 loads or sources.
- Can/should we put OCP on the neutral to the transformer?

Your suggestions and experience will be appreciated. This has additional 
importance as we are preparing to install another 75 kW at the same site 
utilizing 240Vac inverters to the 277/480 grid.

Thanks,
-Kelly
 
Kelly Keilwitz, P.E. 
Principal
Whidbey Sun & Wind
Renewable Energy Systems
NABCEP PV Installation Professional
WA Electrical Administrator
[email protected]
PH & FAX: 360.678.7131



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to