Jerry,
A utility-side cause is a suspicion for our system issue, especially after a 
year and a half of operation. However, in our case the little 15 kVA step-up 
transformers are between the inverters and the main utility inverter for this 
facility. Our design should be robust enough to handle whatever the utility 
throws at it. With the neutral between the 15 kVA 277/480 secondary and the 
utility transformer doing nothing I’m leaning toward disconnecting it - unless 
any of you see a problem with doing so.
-Kelly

Kelly Keilwitz, P.E. 
Principal
Whidbey Sun & Wind
Renewable Energy Systems
NABCEP PV Installation Professional
WA Electrical Administrator
[email protected]
PH & FAX: 360.678.7131



On Apr 3, 2015, at 16:38, Jerry Shafer <[email protected]> wrote:

> Wrenches
> 
> We just had a utility side issue that had the same transfomer damage on only 
> neutral wire. This was a larger 3/0 inverter 333 k but the utility may be a 
> direction to look at. This was one of three systems, none of the others 
> showed damage either. There should be next to nothing on that wire with 240 
> volt inverters.
> Jerry
> 
> On Apr 3, 2015 1:03 PM, "August Goers" <[email protected]> wrote:
> Hi Kelly,
> 
>  
> Sounds like a doozey. As others have posted, it sounds like an imbalance 
> issue. However, it might be possible to solve the problem without replacing 
> the major equipment (could just be wire size, phasing, fuses, etc?). Do you 
> have a single line diagram you can share?
> 
>  
> Best,
> 
>  
> August
> 
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Kelly Keilwitz, Whidbey Sun & Wind
> Sent: Thursday, April 02, 2015 3:19 PM
> To: RE Wrenches listserve
> Subject: [RE-wrenches] PV step-up transformer design
> 
>  
> Wrenches,
> 
> We have issues with a 1-1/2 year old 25 kW grid-tied PV system utilizing 2 
> step up transformers from the array to grid. Actually it’s two identical, 
> 12.5 kW systems (for incentive and financing reasons) on each transformer. 
> Note that the inverter size and voltage selection was also dictated by 
> incentives. Each of the two systems are designed as follows:
> 
>  
> - 3, 3.8 kW, 240 Vac inverters (16A max output current) across each phase of 
> the 240V, 3-ph Delta primary of a 15 kVA transformer. Each inverter 1-ph 
> output has a fused disconnect. The output of all three inverters is combined 
> into 3 phase delta configuration with terminal blocks before the transformer. 
> Other than the inverter AC disconnects there is no OCPD on the 3-ph primary 
> side of the transformer.
> 
>  
> - Transformer secondary to grid is 277/480 wye. The secondary output has two 
> fused disconnects (one at each end of the 600-ft run between array and 
> line-side connection) each with 20-A fuses.
> 
>  
> After more than year of operation we noticed one inverter, in one of the two 
> identical systems, was down (monitoring showed it happened past December), 
> indicating a grid problem. One fuse (of the 3) in the secondary (grid-side) 
> fused disco had blown. Replaced that fuse, but then 2 fuses at the disconnect 
> near the meter, 600 feet away, popped. 
> 
>  
> Systematic checking of the system reveals no shorted conductors, but a 
> problem at the transformer. Close inspection revealed that the insulation on 
> our 90˚C neutral conductor had slightly melted where it touched the X-O 
> neutral wire of the transformer (the splice looked fine). Now it gets more 
> interesting….
> 
>  
> In the last week, while troubleshooting the first 12.5 kW system, its 
> adjacent twin system had an inverter quit with a ground-fault error (these 
> inverters commonly will display ground fault errors for other reasons). One 
> of the 20A fuses in the secondary (grid 277/480) side had popped. And, yup, 
> the neutral wire had signs of overheating. We shut all three inverters down 
> in that system. The transformer doesn’t seem damaged, hopefully because we 
> caught it in time. But we’re looking at a replacement transformer for the 
> first system.
> 
>  
> Here’s what we think may have happened: The grid went down and, on coming 
> back on, the in-rush current to the secondary side of the transformer popped 
> a (undersized) fuse, taking out one leg of the 480. One inverter on the 
> primary side saw a bad grid and dropped out, but the other two connected and 
> kept producing. This unbalanced production resulted in the neutral of the 
> secondary wye (grid) side of the transformer, being overloaded. Over 3 months 
> this unbalanced operation damaged the transformer.
> 
>  
> Initially we replaced the fuses near the line-connection with 60A (it’s a 
> hot-swap and we don’t want those to go again unless the conductors need it), 
> and the fuses near the array transformer secondary with 30A, thinking that 
> will handle the inrush current to the transformer after a grid outage better 
> than the 20A fuses. However, after a lot of discussion, research, and 
> consideration of the risk (of replacing another transformer) we’re wondering 
> if we need to alter the design more substantially. 
> 
>  
> The main design change we’re considering is to replace the fused disconnect 
> on the secondary side with a 3-phase breaker, that will shut off all phases 
> of the grid supply simultaneously in case of an over-current fault. But, what 
> if one inverter just plain quits and that breaker stays on? Will the neutral 
> on the secondary still be overloaded from the other two?
> 
> Other changes we’re pondering include:
> 
> - Do we need a ganged 3-ph breaker on the inverter side, so that all three 
> inverters go off at once? This will only be useful in case of over current on 
> an inverter output, which isn’t likely, and is now addressed with the fused 
> 240 AC 1-ph disconnects on the inverter outputs.
> 
> - Use a step-down transformer in reverse. I.E. use a 277/480 wye primary and 
> 240 delta secondary and back feed the secondary with the PV. Some info from 
> other sources suggest that this will reduce the inrush current from the grid 
> after an outage. I think this would be inefficient at transmitting the PV 
> power.
> 
> - Can/should we remove the neutral connection to the transformer on the 
> secondary side? There are no 277 loads or sources.
> 
> - Can/should we put OCP on the neutral to the transformer?
> 
>  
> Your suggestions and experience will be appreciated. This has additional 
> importance as we are preparing to install another 75 kW at the same site 
> utilizing 240Vac inverters to the 277/480 grid.
> 
>  
> Thanks,
> 
> -Kelly
> 
>  
> Kelly Keilwitz, P.E. 
> Principal
> Whidbey Sun & Wind
> Renewable Energy Systems
> NABCEP PV Installation Professional
> WA Electrical Administrator
> [email protected]
> PH & FAX: 360.678.7131
> 
> 
> 
> 
>  
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to