Hi August,
Yes, it’s difficult to understand what’s going on from my text description. 
I’ll forward a copy of the schematic to all who replied, when I get in the 
office tomorrow. Any wrenches lurking who’d like to look at the schematic let 
me know off-line.
-Kelly


On Apr 3, 2015, at 16:02, August Goers <[email protected]> wrote:

> Hi Kelly,
>  
> Sounds like a doozey. As others have posted, it sounds like an imbalance 
> issue. However, it might be possible to solve the problem without replacing 
> the major equipment (could just be wire size, phasing, fuses, etc?). Do you 
> have a single line diagram you can share?
>  
> Best,
>  
> August
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Kelly Keilwitz, Whidbey Sun & Wind
> Sent: Thursday, April 02, 2015 3:19 PM
> To: RE Wrenches listserve
> Subject: [RE-wrenches] PV step-up transformer design
>  
> Wrenches,
> We have issues with a 1-1/2 year old 25 kW grid-tied PV system utilizing 2 
> step up transformers from the array to grid. Actually it’s two identical, 
> 12.5 kW systems (for incentive and financing reasons) on each transformer. 
> Note that the inverter size and voltage selection was also dictated by 
> incentives. Each of the two systems are designed as follows:
>  
> - 3, 3.8 kW, 240 Vac inverters (16A max output current) across each phase of 
> the 240V, 3-ph Delta primary of a 15 kVA transformer. Each inverter 1-ph 
> output has a fused disconnect. The output of all three inverters is combined 
> into 3 phase delta configuration with terminal blocks before the transformer. 
> Other than the inverter AC disconnects there is no OCPD on the 3-ph primary 
> side of the transformer.
>  
> - Transformer secondary to grid is 277/480 wye. The secondary output has two 
> fused disconnects (one at each end of the 600-ft run between array and 
> line-side connection) each with 20-A fuses.
>  
> After more than year of operation we noticed one inverter, in one of the two 
> identical systems, was down (monitoring showed it happened past December), 
> indicating a grid problem. One fuse (of the 3) in the secondary (grid-side) 
> fused disco had blown. Replaced that fuse, but then 2 fuses at the disconnect 
> near the meter, 600 feet away, popped. 
>  
> Systematic checking of the system reveals no shorted conductors, but a 
> problem at the transformer. Close inspection revealed that the insulation on 
> our 90˚C neutral conductor had slightly melted where it touched the X-O 
> neutral wire of the transformer (the splice looked fine). Now it gets more 
> interesting….
>  
> In the last week, while troubleshooting the first 12.5 kW system, its 
> adjacent twin system had an inverter quit with a ground-fault error (these 
> inverters commonly will display ground fault errors for other reasons). One 
> of the 20A fuses in the secondary (grid 277/480) side had popped. And, yup, 
> the neutral wire had signs of overheating. We shut all three inverters down 
> in that system. The transformer doesn’t seem damaged, hopefully because we 
> caught it in time. But we’re looking at a replacement transformer for the 
> first system.
>  
> Here’s what we think may have happened: The grid went down and, on coming 
> back on, the in-rush current to the secondary side of the transformer popped 
> a (undersized) fuse, taking out one leg of the 480. One inverter on the 
> primary side saw a bad grid and dropped out, but the other two connected and 
> kept producing. This unbalanced production resulted in the neutral of the 
> secondary wye (grid) side of the transformer, being overloaded. Over 3 months 
> this unbalanced operation damaged the transformer.
>  
> Initially we replaced the fuses near the line-connection with 60A (it’s a 
> hot-swap and we don’t want those to go again unless the conductors need it), 
> and the fuses near the array transformer secondary with 30A, thinking that 
> will handle the inrush current to the transformer after a grid outage better 
> than the 20A fuses. However, after a lot of discussion, research, and 
> consideration of the risk (of replacing another transformer) we’re wondering 
> if we need to alter the design more substantially. 
>  
> The main design change we’re considering is to replace the fused disconnect 
> on the secondary side with a 3-phase breaker, that will shut off all phases 
> of the grid supply simultaneously in case of an over-current fault. But, what 
> if one inverter just plain quits and that breaker stays on? Will the neutral 
> on the secondary still be overloaded from the other two?
> Other changes we’re pondering include:
> - Do we need a ganged 3-ph breaker on the inverter side, so that all three 
> inverters go off at once? This will only be useful in case of over current on 
> an inverter output, which isn’t likely, and is now addressed with the fused 
> 240 AC 1-ph disconnects on the inverter outputs.
> - Use a step-down transformer in reverse. I.E. use a 277/480 wye primary and 
> 240 delta secondary and back feed the secondary with the PV. Some info from 
> other sources suggest that this will reduce the inrush current from the grid 
> after an outage. I think this would be inefficient at transmitting the PV 
> power.
> - Can/should we remove the neutral connection to the transformer on the 
> secondary side? There are no 277 loads or sources.
> - Can/should we put OCP on the neutral to the transformer?
>  
> Your suggestions and experience will be appreciated. This has additional 
> importance as we are preparing to install another 75 kW at the same site 
> utilizing 240Vac inverters to the 277/480 grid.
>  
> Thanks,
> -Kelly
>  
> Kelly Keilwitz, P.E. 
> Principal
> Whidbey Sun & Wind
> Renewable Energy Systems
> NABCEP PV Installation Professional
> WA Electrical Administrator
> [email protected]
> PH & FAX: 360.678.7131
> 
> 
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to