I haven't looked lately but check out hardy diesels, 16 kW three cylinder 
Perkins

I have some customers that are real happy with them they have enough power to 
run charging and the household loads of the same time

The price only hurts for a little while

Bob Ellison

> On Apr 9, 2015, at 10:56 AM, Dana <[email protected]> wrote:
> 
> I agree but full load charging usually only lasts but a few minutes as the 
> inverter charge rate drops readily as voltage rises. 8300 watt -10,000 watts 
> or 13000 watts the point is why we are installing air cooled throw away 
> generators that run so fast & hot that they need to be replaced in 2,000 
> hours, not to mention the fuel consumed at 80 MPH?
>  
> Is there a slow speed (1200-1800 rpm) water cooled 8-13 KW generator out 
> there?
>  
> ----------------------------------------------------------------------------
> Dana Orzel
> Great Solar Works, Inc -  NABCEP # 051112-136
> E - [email protected]  - Web - solarwork.com
> O - 970.626.5253  C - 208.721.7003
> "Responsible Technologies for Responsible People since 1988" 
> P Please consider the environment before printing this email.
>  
>  
> From: Jerry Shafer [mailto:[email protected]] 
> Sent: Wednesday, April 08, 2015 7:02 PM
> To: [email protected]; RE-wrenches
> Subject: Re: [RE-wrenches] Question on Back up generators
>  
> We don't install anything smaller then a 13 k its air cooled but works well, 
> as far as the numbers you have, Mine are somewhat different I use max 
> potential load and max potential charge as when the batteries are low the 
> genny must not only supply the home but also charge the bank back up at a 
> reasonable rate, so if the loads are high and the genny only has enough to 
> maintain that load then what about the batteries plus I only use 75% of the 
> genny rating for optimum or improved duty cycle. This is only me and I am 
> sure every shop has there own math.
> Jerry
>  
> On Wed, Apr 8, 2015 at 11:23 AM, Dana <[email protected]> wrote:
> Hey All –
>  
> I just got off of a phone call with my Onan generator supplier. Last 
> conversation with Kohler was the same story basically.
>  
> I was informed that their smallest water cooled generator, the RS22 (22 KW) 
> is now no longer “rated “for off grid. They actually called me to confirm 
> that this generator was for backup power to a utility inter connected house. 
> Tier 4 generators in the EPA CFR 40 is the Federal code what covers this, & 
> you are allowed 100 hours of run time for standby power and maintenance per 
> year.
> Q - Why am I using ridiculous sized generators for something that an 82-8300 
> watt generator does just fine?
> A - The EPA current requirements, a shrinking economy, & manufacturers that 
> have to meet very expensive air quality compliance.
> The Penalty - If you get caught running a “standby power only” generator the 
> fine is now $39,000 per day!
> Now I am far from a polluting kind of individual and all for air quality but 
> this is getting the best of us. The 13KW air cooled generators are only good 
> for 2000 hours, & the water cooled go 20 years of moderate usage but cost a 
> boat load. I hate having the “Generator” talk with a new client they look at 
> me like I am crazy. So the air cooled units are basically throwaways and the 
> 22KW units are way more than we need and what a client needs to spend money 
> on, unless you are at 10,000 ft el.
>  
> If you figure 30 amps/120 VAC input per inverter +/- x 2 = 7.2KW plus say 
> 10-15% fudge or elevation factors would require an 8200-8300 watt generator. 
> Air cooled at 3600 RPM = 80 MPH & 1800 RPM = 40 MPH.  Even if the generator 
> were a bit smaller, ran slow (1200-1800 rpm) and ran a bit longer that would 
> be acceptable.
> So, why are we installing even 13KW air cooled or 22 KW water generators?
> There is a business opportunity here folks.
>  
> What are you all installing?
> Why?
> Is it reliable?
> Would you use it on your house?
>  
> Thanks for sharing all the wisdom and knowledge.
>  
> ----------------------------------------------------------------------------
> Dana Orzel
> Great Solar Works, Inc -  NABCEP # 051112-136
> E - [email protected]  - Web - solarwork.com
> O - 970.626.5253  C - 208.721.7003 - No FAX Line
> "Responsible Technologies for Responsible People since 1988" 
> P Please consider the environment before printing this email.
>  
>  
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to