FYI...

Every [Midnite] SMA E-Panel comes with a shunt trip breaker. SMA requested this when they asked MidNite to design an E-Panel for them. You will need the battery disconnect module to go with each E-Panel though. The battery disconnect modules connect to the Birdhouse and to the shunt trip breakers.

Robin



On 7/17/2015 12:14 PM, Mac Lewis wrote:
Hey Steve,

Yes I'm reading that code article closely and I think its open to interpretation. If you consider PV circuits to include the battery based inverters, you would need to include them in rapid shutdown.

For some reason I thought it applied to all of the DC conductors, including the battery cabling, but it looks like that isn't explicitly called out. Midnites system does have a way to do it.. That will probably show up on the next code cycle.

Thanks for pointing that out.

On Fri, Jul 17, 2015 at 11:30 AM, Steve Jefferson <[email protected] <mailto:[email protected]>> wrote:

    Mac,

    Do you mean to ask for a way to shut down the Sunny Boys connected
    to the Multicluster box?

    Sunny Islands are not applicable to the rapid shutdown
    requirements. They are not PV.

    SMA America, LLC

    Steve Jefferson

    Service Line Supervisor

    3925 Atherton Ave

    Rocklin, CA 95765 - 3714

    U.S.A.

    Tel: +1 916 625 3185 <tel:%2B1%20916%20625%203185> (direct)

    Fax: +1 916 625 0871 <tel:%2B1%20916%20625%200871>

    Mobile: +1 916 622 4253 <tel:%2B1%20916%20622%204253>

    Email: [email protected]
    <mailto:[email protected]>

    www.SMA-America.com <http://www.sma-america.com/>

    cid:[email protected]
    <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be>

    This email and any attachments thereto may contain SMA America,
    LLC confidential, privileged and private material for the sole use
    of the intended recipient. Any review, copying, or distribution of
    this email (or any attachments thereto) by others is strictly
    prohibited. If you are not the intended recipient, please contact
    the sender immediately and permanently delete the original and any
    copies of this email and any attachments thereto. Thank you.

    *From:*RE-wrenches
    [mailto:[email protected]
    <mailto:[email protected]>] *On Behalf Of
    *Mac Lewis
    *Sent:* Friday, July 17, 2015 10:27 AM
    *To:* RE-wrenches
    *Subject:* [RE-wrenches] Rapid Shutdown

    Hi Wrenches,

    I am working on a rapid shutdown design with an SMA multi-cluster
    box with 6 x 6048 Sunny Island Inverters, 2 per phase.  I will be
    utilizing a Midnite system for some roof top combiners.  Is there
    a way to shutdown the Sunny Islands via communication from the
    Midnite rapid shut down box?  Or do I need to do shunt-trip
    breakering?

    Thanks

    Mac Lewis**

    "Yo solo sé que no sé nada." *-Sócrates***

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to