Dear List,
Maybe it's an over simplistic opinion, but shouldnt all sources be
disconnected rapidly in an emergency situation.
We can always do better than what the code requires. I get frustrated when
people go to the book, (and try to hide behind the text).  instead of
thinking through real life scenarios.
There are simple ways to work around these issues.
I find when something is questionable, Ill call the AHJ and get his
approval First.
What would I do in my own house?
What if someone thought all the power was off when they dragged a hoseline
into my basement.
My two cents
Pat

On Tue, Mar 15, 2016 at 1:10 PM, <[email protected]> wrote:

> Ray,
>
> I guess I have to step in after that acknowledgement. PV system circuit is
> a
> self-defined term and therefore cannot be defined unless you are going to
> develop a meaning that is different from the self-definition. It means ANY
> circuit in a PV system. This includes battery and stand-alone circuits in
> the 2014 NEC.
>
> The language of the 2014 NEC was a compromise between the fire service and
> the PV industry.  Originally, the language required essentially
> module-level
> shutdown. I raised the concern with the PV industry to get them involved
> since most were not paying attention at the time. This language was
> developed and intended to cover all circuits in a PV system. In the 2014
> NEC, batteries are part of a PV system and therefore fall under this
> requirement.
>
> In the 2017 NEC, we were very careful to carve out all batteries and loads,
> that were previously part of PV systems, and place them in their own
> articles. Don't shoot the messenger on this one and don't think for a
> minute
> that I alone made this requirement or am alone in interpreting it in this
> way. I did author this compromise with other representatives of the PV
> industry so I think I know what the intent was.
>
> It is understandably difficult for battery systems and I would try to keep
> battery circuits as short as possible. The 5-feet was intended to match the
> requirement of 690.71(H)--which is further evidence of the intent of the
> 2014 NEC.
>
> The 2017 NEC removes batteries from the requirement, but they still cannot
> backfeed the PV array. Energy storage systems (Article 706) will have their
> own requirements in time--that is guaranteed.
>
> Bill.
>
>
> -----Original Message-----
> From: RE-wrenches [mailto:[email protected]] On
> Behalf Of Ray Walters
> Sent: Tuesday, March 15, 2016 9:02 AM
> To: RE-wrenches <[email protected]>
> Subject: [RE-wrenches] Rapid Shutdown
>
> Greetings Esteemed Wrenches:
>
> I've just heard back from our inspector here in Colorado, and we are still
> being required to disconnect the batteries under 690.12.  No where in
> 690.12
> are batteries mentioned, nor in the appropriate 690.71 section that deals
> with batteries.  The entire reasoning behind this is based on a single
> article written by a single person: Bill Brooks.  I have contacted both
> Outback and Magnum on this issue, and their engineers are unaware that
> rapid
> shutdown applies.
> My interpretation is that I could install an inverter and battery system
> that was charged from a generator, and we would not need any rapid shutdown
> at all.  But according to Bill, as soon as I put a single solar module into
> the system, suddenly the entire system becomes PV? The problem lies with
> the
> term 'PV System circuit'  used in 690.12.  690.2 Defines 'PV Output
> circuit', and 'PV source circuit', but there is no 'PV system circuit'
> defined.  690.12 therefore uses an undefined term.
> Our design uses 2 inverters, so if we used Midnite's E panel with their
> remote trip breakers, the 2nd inverter would be more than 5 ft from the
> batteries.  If we used Magnum or Outback DC disconnects (that would comply
> with the 5 ft rule specified in 690.71) they don't offer remote trip.
> We have a Midnite Rapid disconnect Combiner on the roof with the Birdhouse,
> so we are complying with 690.12, it should not be applied to batteries
> though.
>
> Thanks,
>
> --
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Patrick A. Shortell
*Licensed Master Electrician*
*Certified Solar Installer*
71 Oregon Street
Long Beach N.Y. 11561
cell: 516-477-0221
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to