HI Tom,

They are considered 1.2v nominal. 

Charge range is up to 1.7v per cell.
For a 24v system usually you pull out 1 cell or 19 cells 19 x 1.7 = 32.3v
For a 48, usually 2 or 3 , or 37-38 cells.  

If you use much less, then the voltage swings really low, if you go more the 
voltage is too high for most inverters.
The Iota isn’t going to charge them up fully with that low a voltage.  But I 
don’t know if that version Iota is adjustable, many of the older ones had a 
internal pot you could turn up.

But heck give it a try and play with it.  

jay

peltz power




> On Jul 26, 2015, at 4:34 PM, Tom Lane <[email protected]> wrote:
> 
> I have a friend who has forty ( 40 ) Iron Edison Batteries , he says they are 
> each 1.5 volts and wants to use them for a backup to his aquatics business's 
> . Continuous load 24/7 is only 365 watts with surges to 1200 watts . My guess 
> is that ___# of batteries ( maybe 32 to 36 ? ) can be wire as a 48 volt 
> system ? Any suggestion on charge controllers - Morningstar or MidNite ? . .? 
> A Samplex pure sign wave inverter 2000 watts at 48 volts and an Iota 54 volt 
> battery charger is my guess that it might be the way to power the load - any 
> suggestions  . Anyone have experience with Iron Edison .any suggestions 
> appreciated !  Gator tom PS : any suggested websites ? 
> 
> Sent from my iPad
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to