Hi dan

I'm curious why you opted for NiFe vs lithium?

Jay
Peltz power. 




> On Jul 26, 2015, at 8:11 PM, Dan Fink <[email protected]> wrote:
> 
> I made myself a guinea pig on Iron Edison NiFe cells this year, before I try 
> to install them for any customer. I have now about 90 days on them.
> 1.65 volts per cell charging is what they want and need. PV controllers MPPT 
> type are fine with this. just change the settings (assuming the sun is 
> shining) 
> . Inverter/chargers are not fine, at least not my Magnum OMG! over 1.6v per 
> cell!! Overvoltage! Shut down!
> So I have rewired battery bank as recommended by Mrf with 9 cells at 1.2v 
> instead of 10 cells. And now with my 10.8v battery bank I get surge low 
> voltage wonky waveform hits from the fridge turning on, etc. that reboot  the 
> satellite internet, tv etc.
> My plan is to add another 1kw of solar here for an increase of 50% and rely 
> more on the incoming PV that can bring it all up to 1.65v per cell rather 
> than the generator that can't do it thanks to the inverter firmware.
>  I think my new NiFe batteries will do just great in the long run. But their 
> charge/discharge behavior is a continuing lesson. And I am SO glad to learn 
> these lessons myself, instead of in front of a critical customer. 
> 
> 
> 
> Dan Fink
> Buckville Energy
> IREC Certified Instructor™ for: 
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP / IREC / ISPQ Accredited Continuing Education Providers™
> 970.672.4342
> 
>  
> 
>> On Sun, Jul 26, 2015 at 6:55 PM, jay <[email protected]> wrote:
>> HI Tom,
>> 
>> They are considered 1.2v nominal.
>> 
>> Charge range is up to 1.7v per cell.
>> For a 24v system usually you pull out 1 cell or 19 cells 19 x 1.7 = 32.3v
>> For a 48, usually 2 or 3 , or 37-38 cells.
>> 
>> If you use much less, then the voltage swings really low, if you go more the 
>> voltage is too high for most inverters.
>> The Iota isn’t going to charge them up fully with that low a voltage.  But I 
>> don’t know if that version Iota is adjustable, many of the older ones had a 
>> internal pot you could turn up.
>> 
>> But heck give it a try and play with it.
>> 
>> jay
>> 
>> peltz power
>> 
>> 
>> 
>> 
>> > On Jul 26, 2015, at 4:34 PM, Tom Lane <[email protected]> wrote:
>> >
>> > I have a friend who has forty ( 40 ) Iron Edison Batteries , he says they 
>> > are each 1.5 volts and wants to use them for a backup to his aquatics 
>> > business's . Continuous load 24/7 is only 365 watts with surges to 1200 
>> > watts . My guess is that ___# of batteries ( maybe 32 to 36 ? ) can be 
>> > wire as a 48 volt system ? Any suggestion on charge controllers - 
>> > Morningstar or MidNite ? . .? A Samplex pure sign wave inverter 2000 watts 
>> > at 48 volts and an Iota 54 volt battery charger is my guess that it might 
>> > be the way to power the load - any suggestions  . Anyone have experience 
>> > with Iron Edison .any suggestions appreciated !  Gator tom PS : any 
>> > suggested websites ?
>> >
>> > Sent from my iPad
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: [email protected]
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive: 
>> > http://www.mail-archive.com/[email protected]/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to